Discuss Pulsing LED downlights in the UK Electrical Forum area at ElectriciansForums.net

Bjorn

-
Reaction score
0
hi, I am installing two LED down lights under kitchen cabinets. It is a kit supplied by Howdens including a 12v LED power supply. I have run a spur from an adjacent light switch and have put an in line switch in.

When turned on the lights are pulsing every second. I have check the wiring and removed the in line switch but the same issue remains..

Any ideas?

Thanks
 
power supply/driver - LED mismatch take them back and buy from an electrical specialist, not a kitchen supplier.
 
As per Tel post, I reckon the driver doesn't work down to just a few watts. Post up a pic of your power supply if you like :)
 
power supply/driver - LED mismatch take them back and buy from an electrical specialist, not a kitchen supplier.

Actually the LED kits from Howdens are very, very expensive; think they source them from an electrical specialist, then make their mark up.

@Bjorn, firstly have you ensured all the connections are firmly pushed in? How have you 'spur from an adjacent light switch and have put an in line switch in'?
 
It depends if the light switch spurred from has a neutral. (apologies @Bjorn if this isn't the case)

Test the power supply by fitting a plug with a 3A fuse in it and plugging it into a socket.

Howdens do have reasonably good kit, but more expensive for nothing more than what you can get from somewhere like screwfix
 
See more helpful replies.

'Write your reply here.... Make sure your reply is in-keeping with the forum rules, polite and professional. If you disagree with the post(s) above, you can still be professional with your reply'.
 
Sorry, I actually put a junction box in the mains lighting ring and ran a spur that way so I do have a neutral.

Only thing to do is to check the connections in the junction box which is behind the wall unit.

All other connections checked and double checked
 
This is the transformer...

image.jpg
 
Either you have no neutral, as you’ve run it from the light switch giving only line and switch line, or is the switch a dimmer? It may not be LED compatible. I think the first is more likely

It’s a normal switch, I also tried without the switch so it just be something to do with the current
 
Have bypassed the junction box by using alternative connectors and the problem remains.

It must be something to do with the current coming from the lighting ring (now embedded in the wall!)
 

Reply to Pulsing LED downlights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Done a job yesterday, remove old 12v halogens and replace with mains, gu10 downlights. Fitted some LED gu10's no issues. Got a call today saying...
Replies
9
Views
848
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
687
I have three Aurora Fluorescent linkable (linked) under cabinet 'strip' lights (c.21cm each) under the kitchen cabinets and over the sink area...
Replies
2
Views
287
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
190
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock