Currently reading:
PV immersion heater proportional control

Discuss PV immersion heater proportional control in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Have a look at this thread also: http://www.electriciansforums.net/s...ral-heating-linked-monitoring.html#post551986

As far as I WAS aware, the only commercially available proportional control system is the EMMA,

I installed a EMMA SP15/30 a couple of weeks ago, simple to install and seems to be working well.



There is the Immersun device that is proportional and the other that I am looking at theAnthony Wooldrridge sola Controla £395 = vat.See my earlier post but I have repeated the attachment here.
http://www.electriciansforums.net/a...olar-pv-heating-switch-s-g-wooldridge-ltd.doc

Brian
 
Last edited by a moderator:
Re: PV immersion heater switch

Scobo,

Sounds OK and the price(ready to go) is good.
Only thing I noticed after following the link was this:-

The key thing is not to find yourself importing expensive electricity to power the immersion!

Does this mean that if you turn on an appliance (say your kettle) it does not turn off the immersion.
My system uses 2 LDRs. 1 to turn on the immersion/appliance at whatever I set it to, say 1.2kw and the 2nd, that monitors when the red LED in my meter flashes, indicating I am importing power. If this happens the 2nd switch cuts off the power to the immersion

I would be interested to know your set-up performs anyway.




 
Re: PV immersion heater switch

Scobo,

Sounds OK and the price(ready to go) is good.
Only thing I noticed after following the link was this:-

The key thing is not to find yourself importing expensive electricity to power the immersion!

Does this mean that if you turn on an appliance (say your kettle) it does not turn off the immersion.
My system uses 2 LDRs. 1 to turn on the immersion/appliance at whatever I set it to, say 1.2kw and the 2nd, that monitors when the red LED in my meter flashes, indicating I am importing power. If this happens the 2nd switch cuts off the power to the immersion

I would be interested to know your set-up performs anyway.





No, it only has the one LDR to turn the immersion on and off when the power generated is high enough.
This won't usually be an issue as when we're out we have a base load of around 200 watts so I'll calibrate the controller to kick in around 1.5kw and when we're in I could just disable it if there's not enough power to cover the other appliances.
Your setup sounds pretty nifty !
 
Last edited by a moderator:
Re: PV immersion heater switch

Scobo,

Sounds OK and the price(ready to go) is good.
Only thing I noticed after following the link was this:-

The key thing is not to find yourself importing expensive electricity to power the immersion!

Does this mean that if you turn on an appliance (say your kettle) it does not turn off the immersion.
My system uses 2 LDRs. 1 to turn on the immersion/appliance at whatever I set it to, say 1.2kw and the 2nd, that monitors when the red LED in my meter flashes, indicating I am importing power. If this happens the 2nd switch cuts off the power to the immersion

I would be interested to know your set-up performs anyway.




I have not got this device yet but the statement you have raised is explaining that whatever you have connected the Wooldridge device is totally proportional in that it will not import electrcity to suppliment the appliance that is connected to the output of the Wooldridge idealy (THE IMMERSION HEATER).
The Wooldridge will only supply the surplus exported power to the load connected to the Device(THE IMMERSION HEATER).As soon as you turn on anything in the house that exceeds the exported power then the Wooldridge will import nothing to feed to the Immersion Heater. Obviously there will be imported electricity to feed the shortfall of PV to meet whatever appliance you have switched on.
It is not suitable for White Goods Appliances which always require the full 240v ac to function correctly.
Personally I think these proprtional devices are the ideal method of saving money to capture the spare PV power and the Immersion Heater is the perfect load which is ideal for proprtional voltage feeding.
The other is probably storage heaters but you wont have the same savings as the water heating in the Summer months.
 
Last edited by a moderator:
Re: PV immersion heater switch

Brian, Thanks for that. I see what you mean now. Am I right then, in thinking that Scobo's device is similar to mine without the 1st switch with no delay?


Scobo, One thing that would concern me is the size of your system(2.88kw) and the setting recommended to use an immersion(2kw). Your system would need to be performing almost at its peak to supply it. This would be possible on nice sunny days but will struggle through Nov-Feb. I would lower it as you say or maybe more.

I think my system(4kw) will struggle too but, I will test it through the winter months and then reassess things. My base load in the daytime is fairly low(fridge freezer + odds and sods) so, in the winter I may try running my immersion when I am generating say 800w, if it works outs cheaper than using my gas boiler. I guess I could turn the f/f off for a short while to help this.
 
Re: PV immersion heater switch

I don't intend to use the immersion in the winter.
We'll use the boiler as we'll have it on for the heating anyway.
Our base load is around 200 watts and the immersion now runs at around 1kw so I'll have the controller set for around 1.2 to 1.5kw.
There will be dull days when our PV doesn't generate that or not for long enough so the timer will come on to give it a boost.
Our aim is really to save using the boiler during spring/summer to help prolong its lifespan without it costing more.
I realise we won't get completely free hot water with this setup (certainly not this summer) but it should still save a few quid.
 
Last edited by a moderator:
By the time you guys have messed around playing with this and that , you could have saved yourselves a lot of time and possibly imported electricity if you get the settings wrong, by simply buying either the Wooldridge or Immersun devices... both of which I guarantee will have out perfomed your home grown solutions with absolute no concerns about possible import, and no need to change your immersion heaters.

The Immersun has a timer and boost switch, the timer allows you to extend the use of the immersion heater in case the water isn't hot enough at certain times of day and also a short boost button, both of which overide the proportional control if needed. You could also programme you exsiting heating system to provided a hot water boost at the end of the day if needed.

Much Much simpler --- read this post in detail http://www.electriciansforums.net/p...-immersion-heater-regulator-2.html#post562074 and you'll see the actuall difference between proportional and non-proportional systems, also an analysis if the available and used power. The proportional system will give you much greater return in the long term.
 
I have been using Anthony Woodridge's Sola Controlla for the past month and give it full marks. It appears to divert all available energy produced by my 3.3Kw PV not been used by the house to my 3Kw 27" immersion heater. I turned the immersion heater thermostat to max and now have scalding hot water on sunny days (rare at the moment) and acceptable temperatures on even the dullest days.
 
product_image.jpg

I just installed the Mark II intelligent version of solar immersion switch from Intelligent Solar Immersion Switch - Use Surplus Solar PV Power to Heat Water and really happy with the performance. It comes with a differential controller that monitors both PV production and house hold consumption. very affordable price too

Had a chat with the customer support and said they were working on a Mark III with proportional controller as well - don't know if it's true
 

Attachments

  • pv-immersion-heat-control-switch-bright.jpg
    20.9 KB · Views: 172
..................My current supplier Eon, is targeting 1000000 installations to have Smart Meters fitted by March 2014. This may or may not happen but if it does a lot of people will be out of pocket.

Why ??

export is (currently) calculated at 50% of your generation figure and then only paid at ~3p per kw so will have no impact at all. Infact I would go as far to say that if they did monitor your export and it was nil, as you were utilising either sending back through the inverter or using it all, you would still be in pocket as you import at ~12 per KW and you get paid 44p per kw ( or pre DOS day installs do ).......... :smug:

OP I like the sound of these devices as I would like to do this but for me it has to be the right device as its an impossibility for me to have a device thats hard wired in between the immersion heater and the PV system, so needs to be based on RF and/or sensor in my situation, which this sounds like it would satisfy but its over £ 350 + fitting - it may not be worth it....
 
I have been using Anthony Woodridge's Sola Controlla for the past month and give it full marks. It appears to divert all available energy produced by my 3.3Kw PV not been used by the house to my 3Kw 27" immersion heater. I turned the immersion heater thermostat to max and now have scalding hot water on sunny days (rare at the moment) and acceptable temperatures on even the dullest days.

This is what we need Peter, early feedback about this emerging technology. I like this device and am pleased it is performing well.
 
Why ??

export is (currently) calculated at 50% of your generation figure and then only paid at ~3p per kw so will have no impact at all. Infact I would go as far to say that if they did monitor your export and it was nil, as you were utilising either sending back through the inverter or using it all, you would still be in pocket as you import at ~12 per KW and you get paid 44p per kw ( or pre DOS day installs do ).......... :smug:

OP I like the sound of these devices as I would like to do this but for me it has to be the right device as its an impossibility for me to have a device thats wired in between the immersion heater and the PV system, so needs to be based on RF in my situation, which this sounds like it would satisfy but its over £ 350 + fitting - it may not be worth it....

Smart meters are years away - at least 10, as it will cost a fortune for the supplier to replace all the existing meters.

It make sense to use the surplus power flowing back to the grid and why worry when the investment made on the switch is less than 3 months worth of FIT payout (for 4kW).

To me, it's to make the best of the existing situation as I will get the full return of investment in less than 2 years.

Also, it make sense to use the existing immersion wiring from the consumer unit to the immersion itself, as it is stable and solid circut. RF could turn the immersion on, but the question is , can we trust it . After the controller is installed, i could forget it expect it to run for years without any issues. I don't thing a cheap Chinese switching unit will stand a chance for what i want. Also, don't think the Chinese units are CE certified - Not electrical device is suppose to be used in any Europe without CE. Another trouble is a potential patent violation, as they use dual sensors.

Adding to that, the immersion will be switched by a reliable MCB from the consumer unit and the unit my electrician installed does that . Also, the unit from Intelligent Solar Immersion Switch - Use Surplus Solar PV Power to Heat Water looks very simple to install, as it just uses a single sensor to detect and calculate the difference. Also they are CE certified, designed and manufactured in UK and very reasonably priced. Hence the reason I went for it.
 
The immersun appears to do the right job, the question is at what price? Don't post trade price here, if you know, pop it on the Sunlounge.

The website is a little light, so can anyone tell me how it works?

Is it proportional?

How does it wire in?

For those that like to know, Immersun is a product fron 4Eco Ltd 3 Church View, Business Centre, Binbrook, Lincolnshire, LN8 6BY (the immersun dot co dot uk website is regsitered to them) 4ecoltd dot co dot uk
From duedil, the people at 4Eco are:
Jodi Huggett (37), Director, Company Director, 1 Sep 2010 – Present
Robin Barrett (36), Director, Company Director, 1 Sep 2010 – Present
and
Lee Robert Sutton (35) Director, Company Director, 26 Jan 2007 – Present

From the MCS Website:

4eco were MCS Certified by elecsa on 01/04/2010 for:
Air Source Heat Pumps
Ground Source Heat Pumps
Solar PV and
Solar Thermal



Hi MickF
Yes the Immersun modulates the supply to the immersion heater based on detecting the exported excess and feeding appropriately to the immersion heater.
I have contacted Immersun and they have given me the following details of an installer.Immersun will not supply directly to individuals quite rightly because they would not be able to police the DIY installation.
THEY WILL SUPPLY ELECTRICIANS WHO OPEN AN ACCOUNT WITH IMMERSUN.

The follwing details is all I have from one of Immersun's Installers
If you want the name and contact details of this installer and their supply & fit price then PM me as it may not go down too well if I advertise the installer here!•Uses existing immersion heater
•Can control power to any resistive load up to 3kW
•Back-lit LCD display shows: energy saved, load power and mode *
•Volt-free relay contact can be set to operate for additional loads *
•Built-in hot water programmer to set times when water needs to be heated *
•Hot water heater boost function
•Maintains settings and time during power outages *
•Can control boiler for water boost function or use immersion heater *
•Cylinder de-stratification pump control option *
•RS485 MODBUS interface *
•Several units can be linked together to control many loads *
•Can be configured to operate two immersion heaters sequentially *
•OEM units available in a wide range of RAL colours
•Non-invasive grid power monitoring using AC current clamp
•Built-in thermal overload protection
•UK manufactured
•3 Year Product Warranty
•Quality all-metal wall mounted enclosure
 
•Features not available with the immerSUN Lite
[FONT=Atlanta,Atlanta][FONT=Atlanta,Atlanta]Electrical specifications
[/FONT][/FONT][FONT=Atlanta,Atlanta][FONT=Atlanta,Atlanta]Supply: 220-240VAC 50Hz
Power Consumption (excluding load): <1W
Maximum Load: 3.3kW @ 220VAC
Maximum Load Current: 15A
[/FONT]
[/FONT][FONT=Atlanta,Atlanta][FONT=Atlanta,Atlanta]Dimensions
[/FONT][/FONT][FONT=Atlanta,Atlanta][FONT=Atlanta,Atlanta]Width: 155mm
Height: 145mm
Depth: 60mm
Weight: 800g
[/FONT]
[/FONT]
 
So in this day and age you can buy a gas boiler, an Inverter and a chain saw etc all of which could potentially kill you but this company think they need to police the installation of their product -bah, its just another way to get more money out of you !
 
So in this day and age you can buy a gas boiler, an Inverter and a chain saw etc all of which could potentially kill you but this company think they need to police the installation of their product -bah, its just another way to get more money out of you !
I totally Agree,especially as the nearest installer to me is over 40 miles away so the installation adds £250 to the device.
 
Updating my prvious posts on the Anthony Wooldridge Immersion Heater controller which I should be installing in the next two weeks for a trial period.
I attach the other Immersion Heater Controller I am going to trial and is being marketed by ION ENERGY which does everything the Wooldridge device does but adds a few more usefull extras.Also it has a status lcd backlite display.The price is £385 + vat (similar to the Wooldridge) and it is available for self install. It does look rather more professional put together. At the moment they are waiting for CE approval which is expected by August 2012!


View attachment Solar Controller.pdf
 
Last edited by a moderator:
I agree Worcester,when I contacted Immersun they would not deal directly and forwarded my request for details to BPV (see my previous blog 3 days ago) which comes out to £685.25 for supply & install
Interesting though the Ion controller is the same size but the weight is 1130 grms whereas the Immersun controller is quoted as 800grms!!?
 
That's a big difference £462.00 incl Vat to £685.25 (I presume inscludes VAT) just for fitting it.

(That's more than some sparks got paid for a whole PV install !! )
 
That's a big difference £462.00 incl Vat to £685.25 (I presume inscludes VAT) just for fitting it.

(That's more than some sparks got paid for a whole PV install !! )

Thats what I though, yes £ 223.25 inc vat for the install. It would take no more than an hour to install and just half mtr of 2.5mm cable and one isolator. plus the mark up for the device.
 
Gentlemen... It really is rude to discuss a ladies age! Please visit our new website, there will be more technical information to follow
 
Hello all, first post. I've joined as I'm interested to see how these products perform, with a view to installing one to make use of our surplus PV.
 
Hello all, first post. I've joined as I'm interested to see how these products perform, with a view to installing one to make use of our surplus PV.

OK See my earlier post about possible testing the S & G Wooldridge device
.
Due to the lack of printed technical information for the Wooldridge device I have gone with the IMMERSUN Contoller by 4 Eco ltd.
.
I took delivery 7 days ago and I must say this device is very well made.There are two pictures of the device posted on different supplier sites and these may be confusing.The 4 Eco ltd site is the actual production device and is manufactured of steel and powder coated in a beige finish.
I spoke to their technical guy and he confirmed that earlier earlier device was an abs case and that the steel outer case of the production units have a much better durability and is better dispersing any build up of heat.
Ok down to my first impressions. The device comes with all of the necessary fixing fittings and a very detailed User & Installation booklet. Nicely printed and in colour with actual screen shots.

The whole installation took me less than an two hours but you guys out there will be much quicker(I'm the wrong side of 70 & retired!!)

I decided to isolate the Device both I/P & O/P with DP MK grid switches because I have been testing several types of these devices and it does make the whole job neat & tidy and easy to connect.
Now for the results from my observations.

I decided to totally turn off the Gas Central Heating boiler that supplies the indirect cylinder to see if the spare exported surplus power was enough to heat the water.So far it has supplied all that we have required.

I have put a digital thermometer, placed a third of the way down the hot water tank which is sized 1050mm x 450mm just to keep an eye on the water temperature.

I noticed that between the last thing at night 11.30pm and 7am next morning the water temperature had lost on average 20 degrees C.

To rectify this I retro fitted an extra tied on a Mangers tank jacket, even though the tank has original insulation, also foam pipe insulation on all the pipes connected to the tank. This has reduced the heat lost overnight to about 3 degrees.

Back to the IMMERSUN. A weeks useage my impressions are that the device is excellent.I have tracked its output and response time and it reacts very quickly to changing PV output power and changing demand within the house . The temperature of the devices case is very low but the maximum power level fed to the immersion has been a maximum of 2.2 kw due to the lack of sunshine here in Berkshire. I don't think the case temperature will be an issue at all, even at its maximum rating of 3.2kw.
In any event the device has an internal over temperature safety cut off provided to protect the circuitry.
The device has a very clear blue backlite two line display.
When the device is supplying the load with power the display sequences HEATING WATER (Output in Watts);HEATING WATER (Current Time & Date) and (Today Kwh & Total Kwh).There is also a flashing green led in this mode.
When there is not enough exported power to supply the load the led shows orange and the lcd screen shows (Waiting)
When the tank thermostat opens for a full tank of hot water the lcd dispaly shows (Water Hot)
If you want to bypass the exported power to another device when the hot water is satisfied then there is an option to wire several other loads (Storage Heaters etc) via an internal relay contact capable of switching 3kw /16amps.

The is also a Hot water boost function that can also be timed to provive power to the immersion heater if required.
There is also provision to control the Central Heating Boiler to boost the water temperature when the PV exported output is not enough to heat the water.
I can see this facility being very useful in the winter months to give the maximum efficiency of the combined water heating of Gas & Exported power.

All connections to the device are by screw /clamp connectors , all very neat and tidy.

There are two ways of cable case entry, via the bottom with clamp entry glands and via a cut out in the back face of the case but I found you will need to space the device off the wall by about 4mm to give enough extra cable clearance if you are running the cables on the wall surface via truncking( bearing in mind this device will mostly be install next to the consumer fuse box and cable exit to the Immersion heater from the 16A mcb.
I shall be testing this device for about a couple of months and will report back with more results.
Any other info please comment
 
Last edited by a moderator:
Thank you for the detailed review Brian. I have just taken delivery of our first Immersun which will be installed on Monday, and have already taken orders for another two from previous PV customers.
 
Thank you for the detailed review Brian. I have just taken delivery of our first Immersun which will be installed on Monday, and have already taken orders for another two from previous PV customers.

How well did your installation go ? did you install on Monday gr7.My Immersun is performing well, so far I have used 54kwh to heat the water, all of which would have been consumed by the grid with no monitary gain by me because my Solar installation is a free install & maintainence for 25years.
 

Reply to PV immersion heater proportional control in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock