Discuss PV solar surplus energy to immerision devices in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

M

mark@27

Hi

Im a install solar for a small company and a new customer has asked about devices that put any export power into the immersion instead of back into the grid, have looked at several devices like solarimmersion and they say you just clip onto the main incoming tails, put it on a new 16A circuit and connect to the line conductor of the immersion in the CU and that's it no need to adapt the existing circuit.
But surely you would have to remove the thermostat or timer on the immersion circuit as any export energy can only feed in when the immersion is on.

I know this might be a simple question but it will be the first time I've installed done of these and just thought id check

mark
 
I have the Immersun fitted, as my tank ran primarily from the gas central heating there were no timers in situ for the immersion element.
I have to say (when the sun shines enough) the output is very impressive and whilst they can be expensive to buy at the moment they are worth the money in my mind - im hoping to be able to shut off the gas central heating completely from about March/April time as the PV will provide enough output for the hot water we use.
 

Reply to PV solar surplus energy to immerision devices in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
915
We have solar PV panels (1.5kw) and I'm curious about fitting an immersion diverter to use any spare solar energy for heating water rather than...
Replies
3
Views
2K
Hi all I had my PV/Battery setup installed in May and since then all my excess PV is just fed back to the grid for free. When I initially tried...
Replies
1
Views
2K
Renewable energy startup is seeking a Technical Co-Founder to help create a company that is both socially and financially rewarding. The...
Replies
0
Views
1K
V.early days, just had installed solar. No battery, also supply of some parts difficult at the moment so no App or Online monitoring. I have a...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock