M

Morgan keith

We have installed a PV system which has 3 inverters and is protected by a 300mA RCCB. It runs directly back to the main incomer. However there's another circuit which runs from the same point which is protected by a 100mA rcd which is tripping. The 100mA RCD feeds a distribution board which supplies a calf feeder and a couple of sockets etc. Firstly I can't get my head around why a sub-circuit is tripping? Secondly, is there anything stopping us from upgrading it from a 100mA rcd to 300mA to stop the tripping? I've looked at the regs numerous times but nothing's too clear!

Many thanks
 
At the risk of stating the obvious.....are you absolutely sure there isn't a fault with the circuit which is tripping out or the equipment connected to it?
 
Last edited:
Yes. It has been 100% fine for years and the day the PV got installed, it started tripping. The 300mA PV RCD doesn't trip but the other sub-circuit does as it's it's only rated at 100mA. I know it's common for RCD's to trip because of a PV install (hence the 300mA RCD) but am struggling as to why it's tripping if it's on a seperate circuit
 
I can't say that I've ever experienced any problems with RCD tripping being caused by a PV installation - others may have of course. Where a transformerless inverter is used there is, at least in the case of SMA TL inverters, a manufacturer specification that additional RCDs feeding the PV circuit be of 100mA trip rating. Non TL inverters work quite happily with 30mA tripping RCDs.
What make/model are the inverters?
I think I'd still test the 'farm' circuit - that 'it's been working for years' argument doesn't figure 'coincidence' into the equation! :blush5:
 
We have installed a PV system which has 3 inverters and is protected by a 300mA RCCB. It runs directly back to the main incomer. However there's another circuit which runs from the same point which is protected by a 100mA rcd which is tripping.
Many thanks

When you say same point i assume you mean a henley block?
 
have you checked the connections, make sure you've not wiggled something loose a bit on the other circuit during the work?
 
The inverters are Solarmax 15MT. Tested the other circuit and it was fine. Yes runs off a henley block. Turned out to be an issue with one of the inverters so swapped it to a new one and it's good now. Still beyond me as to how it was tripping the other RCD!! But anyways.
Many thanks guys!
 

Reply to PV tripping another RCD on seperate circuit? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
989
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hi all, My 3 month old grid tie inverter has tripped on 3 occasions at startup. Have read plenty of threads here about similar issues but unclear...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock