I might be taking over a job where the previous sparks is not avaliable to finish off 1st fix when the builder needs it...usual rubbish

He had 1st fixed the ground floor- but chased into the block work and clipped cables- no capping or oval- although it is chased in below the surface now (likely not to get damaged by the plasterer) but will it be ok with the sand and cement on top of it?

I know pvc is fine with plaster on it- but not too sure with s+c?

cheers
 
yes it's fine, the one you have to watch out for is polystyrene (insulation board or beads) also known as EPS or XPS as it pulls the plasticiser from the cable.
PU/PIR foam/boards are fine though.
 
When electricity was first discovered and utilised as a power source.people looked at ways to hide the cables that transported those feeble electrons, so they buried the wires under the mortar ;)

In those days (before silent films)the mortar was made with a brew that included Lime,it is a corrosive substance :eek:
It has such a appetite for almost anything that even human bones are seen off by the insatiable appetite

These days the builders of houses and the spreads that cover the walls.they use concoctions which do not include the dreaded Lime :)

In a nutshell,bury your wires in as much sand and cement as you wish,look at them decades later and the chances are it will be unaffected
 
Just the other day I dug out some 6242y from cement render. Not a mark of corrosion there. Probably been there fifteen years. Never seen corroded sheath either in the odd times I have pulled out T&E from cement render. It does say on Doncaster cables they can be embedded but not what in. Also the cable is for dry and damp conditions but not for burying.
 

Reply to PVC cable and sand and cement in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
939
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi all my dad was an electrician and did work on my house in the early 2000s , i had plaster wall lights and am now in the process of redecorating...
Replies
4
Views
2K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
Afternoon Ive just finished PV course and have a question about DC cabling being installed through a house, from the roof to the inverter within...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock