Discuss Queries with EICRs to AMD 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels everywhere...

Just had my NICEIC assessment which was all fine, and during discussion a few things came up where there seems to be a discrepancy between the BBB and Guidance Note 3 (updated)

The NICEIC's view (and mine now I think) is that for EICRs and CU changes on existing wiring, ALL IR testing can now be done L+N->E at 250V

Only on new installation of cabling does 500V IR need to be done, and that before installing any appliances/accessories that might be affected (USB sockets, switches with LEDs, etc)

GN3 seems to support this with the note:
BS 7671:2018+A2:2022 permits the test voltage applied to circuits following connection of equipment to be reduced to 250 V DC, provided that cables were tested at 500 V DC prior to connection.

Although it then goes on to say minimum values of 500V as normal - and add that simple installations with no distribution circuits should preferably be tested as a whole.

The second question I clarified was RCD testing - which the NICEIC assessor (and several sources I've seen) was sure can be done once at 1x, on either 'angle' (0 or 180).

GN3 (updated) still says:

BS EN 61557-6 requires the test current for a tripping test to be applied at the zero-crossing point of the AC wave. Therefore, for each of the tests, readings should be taken with the test waveform starting on both positive and negative half-cycles usually identified ‘0°’ and ‘180°’ on test instruments, and the longer operating time recorded for the 1×I∆n Type AC test.

So which is more correct? The BBB doesn't clarify whether one or two tests at 1x is acceptable....

Finally, the latest triumph in the PRS legislation's many flaws.

As currently enacted, it states clearly:

“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);

Which would suggest that until they bother to pass a new law to change it, EICRs for the purpose of PRS MUST be done to 18th Amendment 1 (even if that happens to be after September when AMD 1 is withdrawn??)

Of course a competent legislator would have got round that by saying 'regulations currently in force', or some such legalese, to avoid more work for bill drafters....

Any one else ---- enough to give a ---- about such things and willing to offer their views?
 
So which is more correct? The BBB doesn't clarify whether one or two tests at 1x is acceptable....
Within the acceptable test result time there is time for many 50hz cycles, many waveforms, so starting testing at 0 or 180 doesn’t make any difference really.
50hz is 0.02 seconds
300ms is 0.3 seconds

I tend to go along the board with the tester set at 1/2 to check they aren’t over sensitive, then go along at x1. Then check test button.
 
Last edited:
The NICEIC's view (and mine now I think) is that for EICRs and CU changes on existing wiring, ALL IR testing can now be done L+N->E at 250V
Agreed, though I’m not aware of many situations where the same test at 500v would cause any harm.
Which would suggest that until they bother to pass a new law to change it, EICRs for the purpose of PRS MUST be done to 18th Amendment 1 (even if that happens to be after September when AMD 1 is withdrawn??)
I had been wondering about that too!
This makes the EICR game even more messy.
 
Finally, the latest triumph in the PRS legislation's many flaws.​

As currently enacted, it states clearly:

“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);

Which would suggest that until they bother to pass a new law to change it, EICRs for the purpose of PRS MUST be done to 18th Amendment 1 (even if that happens to be after September when AMD 1 is withdrawn??)

Of course a competent legislator would have got round that by saying 'regulations currently in force', or some such legalese, to avoid more work for bill drafters....

Any one else ---- enough to give a ---- about such things and willing to offer their views?
My understanding of the PRS legislation is the regs as published in 2018 pre AMD 1 so carrying out EICR's to AMD 1 is technically beyond the scope of the PRS.
I always thought the PRS was a bad piece of legislation at it's draft but we have Emma Clancy the former boss at the NICEIC to thank for it
 
My understanding of the PRS legislation is the regs as published in 2018 pre AMD 1 so carrying out EICR's to AMD 1 is technically beyond the scope of the PRS.
I always thought the PRS was a bad piece of legislation at it's draft but we have Emma Clancy the former boss at the NICEIC to thank for it
Yes looks like you are right! Though to be fair, AMD 1 only had EV stuff in it, so probably didn't change anything to do with testing?

Still if they couldn't even update it for that, who knows when it will be updated to AMD2!

Not sure a prosecution under the act would ever get that far for using a more recent amendment to be fair, although since the main teeth is councils fining landlords who knows. Maybe they are planning to wait a few years and then fine every landlord for having the wrong certificate, and fix local authority funding at a stroke!
 

Reply to Queries with EICRs to AMD 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Sorry if this has been asked a lot but I can’t find the right answer, I will try and explain it the best I can do. I am looking to join a scheme...
Replies
12
Views
2K
Many will by now have heard of the new requirements for private landlords, enacted under Statutory Instrument 2020 No. 312, known as ‘The...
Replies
48
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock