Search the forum,

Discuss Query on recent Electrical Certification for property in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

He says the Zs are too high though, not too low?? Which row is that on the report?

EDIT: Okay House sockets is the 2.1. Kitchen sockets is 0.00, so yes, that would be tripping the breaker repeatedly right, because it's a short circuit? The tenant would certainly have noticed and reported that. Pretty poor that the unit of measurement is not stated too.

In his point 2 he mentions two things, ir at 0.0 (which is wrong) and the high Zs - he doesn't mention the value here, but it is in the table of test results under "measured Zs" at 2.49 ohm. This must be less than 1.1 ohm (max permitted Zs) for this circuit, which it isn't hence the high Zs comment.

His ir at 0.0 is actually both 0.0 and 2.1 somethings in the live-earth column

It cannot truly be 0.0 as this wouldn't just operate the RCD, but would be a major "bang"

I suspect he measured it on the IR setting and never actually measured it again on a more appropriate range.

Technically it is possible to get 0.0 but not trip, as the normal voltage is 230V whilst the test voltage is 500V - so 500V could cause an arc, and show as a short, but 230V may be insufficient to arc, and therefore not trip - although technically possible it's practically unlikely.
 
Strictly speaking exceeding 1.10 isn't overly relevant as it has RCD protection but nevertheless it is too high and likely to be a result of the r2.
 
Strictly speaking exceeding 1.10 isn't overly relevant as it has RCD protection but nevertheless it is too high and likely to be a result of the r2.

Yes, but it's clearly actually faulty wiring, rather than just being unable to bring the Zs in line.

So I would class it as a C2 anyway - I suspect someone has changed a socket or something and not connected the CPC correctly.
 
This is the report when it passed. He's left his original comments at the bottom. You will note some very strange things: ;)


1. 32A Cooker BC still in place.
2. 3 of 5 RCDs still over 40ms at 1x. 2 have reduced to 39ms at 1x.
3. I have asked the tenant for a picture of the garage distribution board cable to see if it's been glanded.

Clearly either the report is a bad copy and paste, with some things changed and some not, or work hasn't been done.

1685557202332.png
1685557258306.png
1685557814210.png
1685557299798.png
1685557376069.png
1685557476581.png
1685557528190.png
1685557639254.png
 
Last edited:
32A on a 10mm is completely fine, no idea why he’s put that down as a C2.

RCD trip time can be up to 300ms, so the 40ms trip time is fine, again not sure why he’s put that down as a C2.

If the SWA hasn’t been glanded the yes this warrants a C2 and will have to be done.

Something that isn’t making sense is that he’s saying there’s a dead short on L-E on your sockets which would mean that your breaker would be going bang every time it’s turned on, which I’m guessing it doesn’t because you would know about this.

This guy either isn’t very experienced with testing or he’s trying to milk money out of you. The only 2 things on there that have to be done are the gland for the SWA and the alleged socket fault, all the others are only C3s and therefore only recommendations. The RCD wouldn’t even be a C3 because it trips well within the maximum time of 300ms so that shouldn’t even be on there
The company sent me an e-mail saying that the guy who did this report has since left. He also suggested that the x1 and x5 results were transposed, i.e. the 23ms results were for 1x and 54ms for 5x. From what I understand about protection devices, this seems very wrong. Or am I wrong?

The address on the form for the company is also different to the one registered at NAPIT?

Is there a governing body for electricians?
 

Reply to Query on recent Electrical Certification for property in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
784
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
958
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock