What you are looking at with 434.5.1 is the "cascading value" for protective devices.It's the exception of 434.5.1 if I understand it correctly. I asked some questions on it a while back and it sounds like it's very unlikely to be an issue due to the resistances between the supply and the fault quickly adding up, lowering it to something more acceptable.
Basically in the domestic case the upstream supply 60-100A fuse limits the peak fault current to a level that downstream domestic 6kA MCBs are able to break even when the measured PSCC is above 6kA.
Also in practice you rapidly lose PSCC as you move away from the CU on any final circuit. Even if you had an infinite PSCC at the supply, to bring it to 6kA needs 38 mOhm and you get that from around 1m of 1mm T&E or around 4m of 6mm T&E.