Discuss Question regarding filling in extent and limitation. Please help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nazoom

Hi

I am trying to fill in the Condition Report Inspection Schedule for Domestic Premiss with up to 100 A Supply. I have a question regarding filling in the Section (5.10) That states Concealed cables installed in prescribed zones. My installation reference method is B and there is no way of finding how deep the cables are or or if they in prescribed zones but they are RCD protected. What is the extent and limitation in this case? Is it 100% limitation or 50%? Or is it N/A? I know that i have to mention it in section D (extent and limitation) of the report.

Many Thanks
 
are you sure its ref method B ?
clipped direct to wall is ref C

anyways , you dont have to write anything in the report for cables in walls & floors that you cant see , its already noted on the first page of the eicr under limitations - have a look.

the inspection sample rate of 30% 50% or whatever , is for accessories such as lights , sockets etc , its not for cables as most houses only have about 2% of visible cable on show.


in the section " cables in prescribed / safe zones " , just write N/V ( not verified )
 
are you sure its ref method B ?
clipped direct to wall is ref C

anyways , you dont have to write anything in the report for cables in walls & floors that you cant see , its already noted on the first page of the eicr under limitations - have a look.

the inspection sample rate of 30% 50% or whatever , is for accessories such as lights , sockets etc , its not for cables as most houses only have about 2% of visible cable on show.


in the section " cables in prescribed / safe zones " , just write N/V ( not verified )

Glad you clarified that for the OP biff, have an awful vision of him smashing the gaff to bits for inspection lol.
 
I am sure the reference method for erection is B as the cables are concealed in the walls and protected by 30 ma RCD. So I ll take your advise as N/V. And there is no further investigation required?

Many Thanks.
 
Last edited by a moderator:
I am sure the reference method for erection is B as the cables are concealed in the walls and protected by 30 ma RCD. So I ll take your advise as N/V. And there is no further investigation required?

Many Thanks.

Ohh ye of little faith, Biff gave you the answer, and you are doubting it...naughty boy.

Here is a recently posted article on reference methods that YOU will find useful http://www.electriciansforums.net/i...lations/70017-reference-method-explained.html
 
Sorry to bother you again!

I still have a problem with this question. I am not sure whether this would require Further Investigation or not?

Sorry again biff n many thanks.
 

Reply to Question regarding filling in extent and limitation. Please help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Guidance please - C&G L3 electrical installation - Hotel extension project Hi folks, I am fairly new to this forum but it looks like the...
Replies
6
Views
758
Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...
Replies
8
Views
1K
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock