A

Andy_S

Hi, new to the forum but have found it to be a great source of info in the past. I am qualified to 16th edition but as i'm a maintenance engineer and mainly work on machinery rather than domestic installations i'd like to ask the following questions to make sure i get it right!

I'm looking to replace my consumer unit, a 60A Wylex rewireable with minitrip bases fitted, fed by what appear to be 16mm tails.

I have asked the DNO to fit a double pole isolator so i can work on a de-energised system, If i feed my new CU with 25mm 6181Y will the DNO have to upgrade the cable from the cutout to the meter and from the meter to the isolator. If so, is this additional work chargeable or will i get a freebie as i'll be paying (through the nose ) for an isolator. I have a Western Power Distribution / N-Power combo, TNC-S supply.

I'll also be replacing my main earth with 16mm, and the bond to the gas and water pipes too. Will it be ok to clip the 10mm earth direct to the exterior of the house to go from front to back with out mechanical protection, i have a half rendered house and the cable will be hidden nicely by clipping up under the bellcast stop beading?

I will be having a PIR done to make sure all is ok but want to get most of the donkey work out of the way.

Thanks in anticipation!
 
Why are you intending to install 25mm² conductors?
If it's only a 60A supply, 10mm² will most likely be sufficient.
It's unlikely that the DNO will replace conductors for free, unless they're damaged or show sings of overheating.
As for upgrading them, why would they need to do so?
 
Will Clarify, existing CU that i want to replace is 60A rated fed by 16mm tails. Want to fit 100A rated CU which will require 25 mm tails. Think the DNO's cut out is 100A, though.
 
the cut out may say 100A on the outside, but it's anybody's guess what's inside the black magic box.
 
Bit of a result, Npower's metering agent will fit a DP isolator between the meter and the CU free of charge. DNO don't seem concerned about conductor size either side of the cut-out, especially as i'm not increasing load :D.
 
if it's a meter fitter fitting the isolator. i'd be certain to check the polarity of the tails after.!!!!!
 

Reply to Questions on new CU, Tails and Earthing. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
968
Hi, need more advise as getting two different views from electricians. Ty Detached double garage 10m from house, split equally into garden room...
Replies
3
Views
254
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
980
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
904
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock