the pict

-
Mentor
Reaction score
247
We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
 
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
 
We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
 
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
OK lets take some actual numbers, Ze or Zdb .22, on the ring Live .45. CPC .76 So 1.21 / 4 = .30 That figure is only used to check around the RFC for higher than expected readings It goes nowhere on the cert, what does go on the cert is the sum of ZE & R1+R2 which is 1.43 which is Max measured ZS only its not, its the
sum of the readings, to get a measured ZS its a live test done at a socket as that is the only real result . However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer
 
However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer

No, the max measured is the maximum value which has been measured.
A measured value is not calculated, it is measured.
 
If you have measured all tests correctly on a ring final circuit & checked the r1 + r2 /4, you will have all the necessary check sums & measured results ( Ze, Zs Zdb) to fill out the cert. So whats the problem ! Maybe( R ) Stands for Radial !
 
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
It's plainly written down in GN3 and other readily available publications. can you tell me the page
 

Reply to R1 R2 Chestnut time again in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, in the UK, was vacuuming, did upstairs, went down to the hall, and the vacuum stopped.. checked the fuse, fine.. hit it, plugged it in...
Replies
13
Views
399
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
681
Here we go again, another job that has had a council inspection, different council to last time but still perplexing. The problem with these jobs...
Replies
14
Views
1K
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
25
Views
1K
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
756

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock