- Reaction score
- 5,607
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'.
It doesn't look well written at all. However, what I cant understand is the very high quote when there is only 1 x C2.
My thoughts...
1. Nothing written in 'general condition of installation.
Just seems poor not to write anything.
Observations page...
2. 'Earth and neutral connections not in correct order'
I don't know what this means?
3. Light fitting in top room hanging by cable. (They have put C3, I would put C2. Difficult to say without seeing it.)
4. Single insulation showing C3 (I would rate this as C2)
5. O/S light no cover and exposed to weather C3 (I would put C2)
6. Downlights in bathroom not correct IP C3 (I would put C2)
Other bits of the form I'm not happy with...
7. Where it says 'agreed with' they have put N/A
8. PFC = 0.1kA (but Ze is 200ohms)? Should be 0.001KA
9. Ze = 200ohms but a large variance in the Zs results from 198ohms - 244ohms? This in itself is odd, but I have forgotten if the Ze needs to be 200ohms or less, or if it is the Zs that needs to be less than 200ohms? Also, seems rather unlikely the Ze is exactly 200.
Another point... Is this form acceptable. Shouldn't it be one that is updated to Amnd 2 (2022)?
Test results page
10. Missing R1 + R2 results
11. Odd R1 +R2 results 0.01, 0.02??? far too low.
12. No IR results whatsoever.
It doesn't look well written at all. However, what I cant understand is the very high quote when there is only 1 x C2.
My thoughts...
1. Nothing written in 'general condition of installation.
Just seems poor not to write anything.
Observations page...
2. 'Earth and neutral connections not in correct order'
I don't know what this means?
3. Light fitting in top room hanging by cable. (They have put C3, I would put C2. Difficult to say without seeing it.)
4. Single insulation showing C3 (I would rate this as C2)
5. O/S light no cover and exposed to weather C3 (I would put C2)
6. Downlights in bathroom not correct IP C3 (I would put C2)
Other bits of the form I'm not happy with...
7. Where it says 'agreed with' they have put N/A
8. PFC = 0.1kA (but Ze is 200ohms)? Should be 0.001KA
9. Ze = 200ohms but a large variance in the Zs results from 198ohms - 244ohms? This in itself is odd, but I have forgotten if the Ze needs to be 200ohms or less, or if it is the Zs that needs to be less than 200ohms? Also, seems rather unlikely the Ze is exactly 200.
Another point... Is this form acceptable. Shouldn't it be one that is updated to Amnd 2 (2022)?
Test results page
10. Missing R1 + R2 results
11. Odd R1 +R2 results 0.01, 0.02??? far too low.
12. No IR results whatsoever.
Last edited: