Discuss Amending EICR report from unsatisfactory to satisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
3
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being written on the report which you'd expect. Completed all the remedials and the QS has come back and passed them all off, but will not put SATISFACTORY on the report! Up until mid last year this was always the case and I'd get the SATISFACTORY comment on my paperwork, as I work for the council and they kind of demand seeing it, but this firm wont put this on despite their being no safety concerns at all. Has something changed in the regulations regarding this, as they're telling me they can't amend the original paperwork? Please advise?
 
Nothing has changed it has always been the case. The Report was unsatisfactory as per the date of the document you can't suddenly change it. You either have a new EICR or you append any certification from the remedial works to the old EICR.
 
Nothing has changed it has always been the case. The Report was unsatisfactory as per the date of the document you can't suddenly change it. You either have a new EICR or you append any certification from the remedial works to the old EICR.
That's interesting. So in your opinion, the previous NICEIC testers were incorrect in re-issuing the cert as SATISFACTORY?
 
Maybe the installation was satisfactory in the past, but now there is a problem: breakdown of insulation, broken equipment etc that requires repair…
Once those repairs are made, and a certificate covering the repair is produced…. Then the certificate can be appended to the EICR to prove whatever made the report unsatisfactory has been dealt with.

Some unsatisfactory issues can be repaired simply while doing the report… loose cables etc….


Unfortunately, some institutions just demand a satisfactory report… nothing else.
 
That's interesting. So in your opinion, the previous NICEIC testers were incorrect in re-issuing the cert as SATISFACTORY?

They were indeed incorrect, the same report can't have 2 different outcomes. The report details the condition of the installation at the time of testing.

Any remedial work carried out should be certified with the appropriate certificate. If no certificate applies (eg fitting a blind grommet to a hole) then a written record of the work done should be kept.
 

Reply to Amending EICR report from unsatisfactory to satisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Hi all, have just ordered my first EICR ever for a studio to 1-bed conversion flat in London. It cost a little less than £80 and the electrician...
Replies
51
Views
8K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
605
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
883
New to this forum. Just received the first EICR report which is unsatisfactory (C2 and FI issues below). The electrician quoted for another £300...
Replies
31
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock