Discuss radial and ring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
4
Hi everyone I've come across a weird situation where somebody has got new sockets added, but from the board it is a radial in 6mm as there is one set of cables into the breaker, then when you look at the sockets (2 double sockets) it's got 2, 2.5mm cables going into both like it's a ring
Does this seem acceptable

I have drawn what I think has happend and if anyone thinks it's acceptable

14489881011481906294751.jpg14489881011481906294751.jpg
 
Commonly known as a lollipop circuit, its not a standard bs7671 paint by numbers circuut so you have to actually think about it a little when it comes to testing it
 
It's a lollypop circuit. Perfectly acceptable providing that all the usual requirements are met regarding overcurrent protection, RCD protection, Zs, ring continuity, etc, etc.


Edit: Snap!
 
Ok thanks guys it's not acceptable with a 40 amp breaker tho isit because the ring should be be 32 amp max breaker shouldn't it
it should be on a 32A MCB. soon chamge it. otherwise, as before. if readings are OK.....
 

Reply to radial and ring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
257
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
658
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
682
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
485
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
710

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock