- Reaction score
- 25,583
No it shouldn't be on a 32A protective device.
Discuss Radial Circuit Cable Length in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Many thanks for the confirmation, I did ask him to put a 20 amp MCB in instead but he was adamant that there was nothing wrong with using a 32 amp MCB & when asked about the cable running in conduit he said those are guidelines only & not rules.No it shouldn't be on a 32A protective device.
He is incorrect.Many thanks for the confirmation, I did ask him to put a 20 amp MCB in instead be he was adamant that there was nothing wrong with using a 32 amp MCB & when asked about the cable running in conduit he said those are guidelines only & not rules.
Also because not all of the run was in conduit these "guidelines" do not apply.
Am I correct in saying that this is not the case?
He is incorrect. We cannot pick and choose which regulations we want to comply with or not. The cable rating for 4mm2 in conduit is at best 30 amps. If grouping is also a factor then it's even less.He is incorrect.
He is incorrect.
He is incorrect. We cannot pick and choose which regulations we want to comply with or not. The cable rating for 4mm2 in conduit is at best 30 amps. If grouping is also a factor then it's even less.
So a 20 or 25 amp MCB is needed.
Reply to Radial Circuit Cable Length in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
We use essential cookies to make this site work, and optional cookies to enhance your experience.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.