L

lost-sole

Came across this problem at weekend brandnew range installed 40amp mcb on RCD side of split load board. Cooker isolator is 2 gang with socket out let. The rcd trips when ovens are on I know the reasons but was wandering how you go on with regs as all i could do was move mcb over to none rcd side of board so now you have a socket in a kitchen thats not got rcd protection do I

1. change cooker isolator to one gang without socket, don't think owner would be too happy as it would require backbox to be moved and some more tiling.

2. label socket outlet warning notice etc

3. Become a joiner!!!
 
as i remember you can supply a fixed piece of equipment from the non rcd side, and can you not label the socket as a non rcd protected socket??
 
it is a beast 3 ovens, i mean i had all 3 switched on so it must be the eliments doing it. as regarding supplying fixed equipment from non rcd side not sure if this is right on this occasion as portable equipment can be plugged into the socket outlet and trust me this guy is a solicitor and no common sense so you can bet your life he'll plug a garden chainsaw into it and chop through the cable or something
 
it is a beast 3 ovens, i mean i had all 3 switched on so it must be the eliments doing it. as regarding supplying fixed equipment from non rcd side not sure if this is right on this occasion as portable equipment can be plugged into the socket outlet and trust me this guy is a solicitor and no common sense so you can bet your life he'll plug a garden chainsaw into it and chop through the cable or something

have you done an IR test on it?

i suppose techincally you could label it for one item of equipment, but what? "Kettle only", "electric can opener only"

Difficult one, i would be more tempted to try and sort out the problem, it shouldnt be tripping an RCD
 
hi, was called out to a sim fault.. customer said mfi had fitted the kitchen and oven and when the oven was switched on it would trip the rcd.

Found the oven wired in at the consumer unit on a 32A mcb on the rcd side but the nuetral was connected on the non rcd side! which would cause the rcd to trip when current would flow..

hope that helps? worth a look, easly done ;)
 
hi, was called out to a sim fault.. customer said mfi had fitted the kitchen and oven and when the oven was switched on it would trip the rcd.

Found the oven wired in at the consumer unit on a 32A mcb on the rcd side but the nuetral was connected on the non rcd side! which would cause the rcd to trip when current would flow..

hope that helps? worth a look, easly done ;)

Have had the exact same thing about 4 weeks ago. DIYer.
 

Reply to Range cooker tripping RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
953
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
837
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top