Discuss Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again

Would i be correct in saying the DNO will need to be notified and called out?
 
Last edited:
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.

Would i be correct in saying the DNO will need to be notified and called out
?????????????????????????????????
 
Sounds like the DNO lead sheath is not providing a good earth path, and if the readings stay the same regardless of protective bonding connected or not, then the gas/water supply pipes are probably plastic and therefore not providing any earth.
Contact the DNO to sort their cable
 
Was the main Earth dissed from the CU when you tested Ze why mess with the Main bonding? after all you are testing the earth fault impedance with the main earth dissed. aren't you?
Yes he is testing 3 Phase but the principle is the same for SP&N
 
Yes but let's assume the Ze is/was 3.25 Ohms fine, however whether I connect the bonding or not this will make not a jot of difference. It is somewhat confusing the description of the scenario. In any event if the external impedance is that high, then yes of course the DNO must rectify it. However they could say there is no earth someone put that BS953 clamp on and it's nothing to do with us we only have to maintain an earth we supply. In which case it's tough TT for you.
 
OK now this is getting confusing can someone explain to me when doing a Ze what has bonding to do with the price of eggs.
forget the bonding mate i was saying it out of interest can we just get back to the point, the Ze is high with the main bonding disconnected, i assume the DNO will need to be notified and if so are they obliged to repair the Poor earth
 

Reply to Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock