Discuss RCBO not tripping from over-current in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Just curious, has anybody else dealt with this?
16a Hager RCBO exceeding well above it's rating and for a long period of time.
 

Attachments

  • PXL_20240214_024843158.MP.jpg
    374.8 KB · Views: 34
  • PXL_20240214_024634129.MP.jpg
    318.4 KB · Views: 32
I’ve had experience of old mcbs getting stuck on after being pushed even near their limit to the point that a 16A could carry even twice that at times.
You could flick the switch off and the contacts inside remained closed.

Does your RCBO switch on and off as normal, ( and does the switch feel “soft” compared to others?) And does the test button work on it ok?

What is causing the overcurrent? Can equipment be removed from the circuit, or can the circuit design allow the RCBO to be replaced with a 20A version?
 
If you look at the trip time/prospective current graph (Fig 3A4 on page 370 of the big blue book - assuming it's a 60898/61009 compliant device with a Type B curve), at 20A that device probably won't ever trip until it gets tired from years of running at it's maximum capacity.
The hager graph for B curves gives an upper and lower limit. This overcurrent sits in the middle of those lines as they dissapear off the top of the graph, so it may or may not trip eventually
 
It will be rare but the piston through the overload tripping coil maybe subjected to contamination and stopping or slowing the piston moving as it should.
 
I’ve had experience of old mcbs getting stuck on after being pushed even near their limit to the point that a 16A could carry even twice that at times.
You could flick the switch off and the contacts inside remained closed.

Does your RCBO switch on and off as normal, ( and does the switch feel “soft” compared to others?) And does the test button work on it ok?

What is causing the overcurrent? Can equipment be removed from the circuit, or can the circuit design allow the RCBO to be replaced with a 20A version?
Yeah, I thought it might have seized inside, as it was only noticed after the storms here in Victoria. I was thinking of a possible surge may have damaged the mechanics inside the RCBO, but after changing it over for a new Hager RCBO, the issue is still there.

Prior to this, I had even plugged the two 10amp heaters (which were plugged into a single 10a double gpo) on another circuit to see if it would trip, with no success. We even had an older sparky come out and have a look at what he thinks and he didn't batt an eye, however a few other mates who are sparkys say the same thing I said, "it should have tripped".

The circuit normally has a printer on it, which barely draws anything, but one of the office staff plugged a couple of heaters in to dry up the carpet as it flooded the night prior. Upon walking into the office, I made this discovery and looked into why it wasn't tripping. These heaters had been running for roughly 4hrs.

I'm starting to think the Hager brand might just have a much higher tolerance, but kinda defeats the purpose.
 
If you look at the trip time/prospective current graph (Fig 3A4 on page 370 of the big blue book - assuming it's a 60898/61009 compliant device with a Type B curve), at 20A that device probably won't ever trip until it gets tired from years of running at it's maximum capacity.
That's crazy. I didn't have a load tester, but I'm questioning at what point will this RCBO actually trip. I only saw it at 21a, but depending on your derating factors, this is already in the area of not actually protecting the 2.5mm tps.
 
It will be rare but the piston through the overload tripping coil maybe subjected to contamination and stopping or slowing the piston moving as it should.
Yeah, I thought it might have seized inside, as it was only noticed after the storms here in Victoria. I was thinking of a possible surge may have damaged the mechanics inside the RCBO, but after changing it over for a new Hager RCBO, the issue is still there.

Prior to this, I had even plugged the two 10amp heaters (which were plugged into a single 10a double gpo) on another circuit to see if it would trip, with no success. We even had an older sparky come out and have a look at what he thinks and he didn't batt an eye, however a few other mates who are sparkys say the same thing I said, "it should have tripped".

The circuit normally has a printer on it, which barely draws anything, but one of the office staff plugged a couple of heaters in to dry up the carpet as it flooded the night prior. Upon walking into the office, I made this discovery and looked into why it wasn't tripping. These heaters had been running for roughly 4hrs.

I'm starting to think the Hager brand might just have a much higher tolerance, but kinda defeats the purpose.
 
Do the heaters have thermostats in them? They could be switching on and off so the full 20A is only being pulled for short periods,
 
Do the heaters have thermostats in them? They could be switching on and off so the full 20A is only being pulled for short periods,
Here's the heaters. I don't believe they do have a thermostat inside them.
 

Attachments

  • PXL_20240220_023600197.MP.jpg
    357.4 KB · Views: 15
  • PXL_20240220_023551414.MP.jpg
    385.1 KB · Views: 15

Reply to RCBO not tripping from over-current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
894
I have a small caravan park with 8 pitches. Each have a Rolec Electrical Hook-Up unit fitted with a Rolec 16A Single Pole and Neutral 2 Module C...
Replies
14
Views
2K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
800

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock