and another thought. check if there is any sort of continuity between one ring and another. it's within the realms of possibility that you have a neutral borrowed from one ring to another.
 
i have the same kind of fault but with a rcd, even if i plug something into the ring with the mcb turned off it still trips the rcd, going back this weekend to have another look, i'm going to clamp meter the cpc to check for any high current there , let us know how you get on
 
and another thought. check if there is any sort of continuity between one ring and another. it's within the realms of possibility that you have a neutral borrowed from one ring to another.

If you had a borrowed neutral wouldn't the "other" ring also be suseptible to tripping?
 
Yeah definetly connected properly. These ones, type B have no functional earth.]


Yes they do.

Its to provide an electrical path when you press the test button. That's why its coloured cream and not green and yellow.

I think you'll find the test button is purely mechanical, just releasing the latching mechanism.
 
Last edited:
My point is that the test button creates an imbalance between line and neutral, through a resistor and checks mechanical operation only, it does not check or use any part of the earth system.

Pedantic yes but guys studying 2330, 2391 etc. need this level of accuracy.
 
I think there was an issue with your quote tags, it looks like you're arguing with yourself :)
 
Have a look at this video.

Typical!!! another manufacturer trying to cut there costs with there own misleading information. They want to remove a function that saves them money, but not you!!
Then go on to try and convince you that it's time and money saving for the contractor.
Not a mention that those RCBOs without the functional earth lead will cost any less than those With, that's because there isn't any cost saving...

It's all Money, money, money these days, paying more for less is the order of the day!!!!
 
Where in the OP does it mention Double Pole?

I'm explaining that the earth fly lead is used in the event of a lost supply neutral but in the case of double pole devices this is not needed because in tripping condition, the neutral will also be isolated.

That is why many BS 61008 RCD's do not have an earth fly lead.
 

Reply to RCBO problems in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top