hey all

i was wondering what reason would be behind an RCBO tripping out before the ramp test has finished and comping up with trp?

thanks
 
Not sure what you mean with"before the ramp test is finished". The whole purpose of the ramp test is to find out what current will cause the device to operate, when your meter comes up with trp it should have some more info on there for you.
 
what i mean is when i drop my test leads on the rcbo and press test. the rcbo will then trip out and the meter will say trp on the screen giving no result. the tester its a megger mft1552

ive changed the rcbo as well

all other rcbo's trip within in limits
 
You are getting confused here with X.5 / X1 / X5 test and ramp testing you shouldn't need to ramp test a rcd unless you are trying to resolve tripping issues.
 
i am trying to resove tripping issues
So there's nuisance tripping on one RCBO?
What happens on the half test? If it's tripping immediately on a ramp I'd expect it to be but as Murdoch said have you made sure that all loads are removed and the IR is ok?
 
i have and the reading was appauling between n and e, also all 27 lights have their own joint boxes burried under a garden spanning over 100 meters.
 
to add to the last reply between neutral and grey (spare core), which will be used as a live is also down, which has nothing connected to it as of yet
 
probably tripping due to fault on circuit and 1552 is aborting test.
 
Leave the garden lighting circuit off (physically disconnected)for a week if it stops tripping then probably water ingress in the fittings or joint.
 
well thats what i thought, but i sealed them pretty well in galv boxes covered in magic gel, been ok since christmas and had a lot of rain in that time
 
So this immediate tripping on a ramp is after you have disconnected the circuit completely? Also the cables are failing their IR?
You have a couple of problems in this scenario.
 

Reply to rcbo tripping before ramp test is complete in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Folks. I need to install a defib unit outside on a wall. Does this require an RCBO or not, just wondering as the unit has a small heater within...
Replies
15
Views
531
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
777
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
480
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock