Check any hard wired appliances like boilers, extractor hoods etc are disconnected as well. Not just switched off.
o_O That's a good idea. Ill isolate the fans, cooker hood and boiler from the circuits and see what happens. That maybe the reason. I find when I fault-find I always look at the worst case and take them apart instead of just looking at the simple possibilities. It wastes a lot of time
 
I was fault finding a circuit last week because a switch had stopped working - on the switch drop there was no continuity on any of the 3 cores , IR at one end was OK, but at the other end the IR had a dead short N-E.

A new set of shelves had been put up......

A drill had gone through the cable completely!

The end of the cable with the dead short wasn't connected to anything so wouldn't have shown up on any tests .....

Given its a kitchen circuit, has Kev the fitter damaged a cable for you?
 
I'm assuming that the IR tests you've carried out have all been fairly short tests... press the button, get the result kind of affair?

Can you continue the test, maintaining the 500v for a while?

I've had a couple of cases where the test appears to be satisfactory, but if you apply the test voltage for a longer time the charge builds up to a point where it jumps a pinhole in the insulation and the IR momentarily drops. Not so easy to see on digital test gear if there isn't a virtual analogue display, but visible on my Megger's virtual analogue meter in the LCD.
 
I think this may be the case as well. Will need to head over there again and spend a couple of hours testing the rest of the circuits one last time

To help us mull over this problem could you tell us the type of supply and earthing system, the presence and state of EP bonding and provide a picture of the intake and CU innards please?

As Murdoch said, it would be really helpful if you could borrow an earth leakage clamp meter to do some measurements, for example standing leakage for each final circuit, and then total leakage less kitchen FRC, and then finally total leakage for all FCs.

Also could you post some figures for your measurements of IR?

Is all the wiring and are all the wiring accessories on the kitchen ring new? Have there been any water leaks?
 
Last edited:

Reply to RCCB tripping when under load problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Rcbo tripping on 1/2 settings with load connectted but ok when load disconnected all other tests are fine… FI required but any thoughts on this😎
Replies
10
Views
799
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
726

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock