Discuss RCD and replacement fails to operate in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
On completion of some recent minor work , I carried out the usual testing and noticed the incoming 100A 30mA rcd on the Consumer unit was failing to trip at X1 and X5 at both 0 & 180 degrees Further investigation revealed that the test button on the device failed to trip it as well . All well and good so far faulty RCD me thinks . How often do these devices actually get tested by the end user (despite the quarterly test label ) Replaced it . Checked again and although test button now trips, it still fails to pass RCD ramp or time tests ? Just in case the replacement unit was faulty ( however unlikely ) , I had another unit on the van changed that out with the same result .
Earth loop impedance testing on both on the ring final and incoming Ze, very low reading less than 1 Ohm bearing in mind this is a TT installation ( does seem exceptionally low,) I have checked all round the incoming supply head no sign any PME link I may have missed ????

Any ideas fellow sparks
 
On completion of some recent minor work , I carried out the usual testing and noticed the incoming 100A 30mA rcd on the Consumer unit was failing to trip at X1 and X5 at both 0 & 180 degrees Further investigation revealed that the test button on the device failed to trip it as well . All well and good so far faulty RCD me thinks . How often do these devices actually get tested by the end user (despite the quarterly test label ) Replaced it . Checked again and although test button now trips, it still fails to pass RCD ramp or time tests ? Just in case the replacement unit was faulty ( however unlikely ) , I had another unit on the van changed that out with the same result .
Earth loop impedance testing on both on the ring final and incoming Ze, very low reading less than 1 Ohm bearing in mind this is a TT installation ( does seem exceptionally low,) I have checked all round the incoming supply head no sign any PME link I may have missed ????

Any ideas fellow sparks
Are you sure it's not a 100mA rcd main switch?
Being a tt
 
Is this problem because it's a TT or because as Tel says 'a neutral earth fault' within the installation. I'm interested now.
 
True unless that anomaly of N/E relationship that has been mentioned in past that will cause RCD not to trip in normal operation.
 

Reply to RCD and replacement fails to operate in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
892
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
614
Many years ago I fitted some RCD socket outlets to my parents home for the two likely to be used outside, the front hall and the kitchen one next...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock