Discuss RCD before a 230v/24 PSU? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all

I have seen a schematic drawing for a control panel recently where they (whoever drafted the drawings, designed the panel) show a RCD before the 230v/24v dc PSU, and the PSU is the only device downstream of the RCD

in my mind this has no merit. The 24v secondary d.c side of the PSU supplies electronic circuits

would you guys agree that the RCD is this instance serves no valuable function?

thanks
 
would you guys agree that the RCD is this instance serves no valuable function?
It depends, but in many cases no.

If the power supply has full safety separation (PELV, etc) then probably not, but it also might depend on any other risk factors that might impact on isolation: such as operating in an environment with the risk of water leaks, extreme condensation, or conductive dust, etc.

Also in might depend if the RCD is for the whole system and in a separate double-insulated box as it is part of TT earthing for the control panel, and serves to protect against cable damage on route to the PSU, etc.

TL;DR it needs a bit more context
 
It depends, but in many cases no.

If the power supply has full safety separation (PELV, etc) then probably not, but it also might depend on any other risk factors that might impact on isolation: such as operating in an environment with the risk of water leaks, extreme condensation, or conductive dust, etc.

Also in might depend if the RCD is for the whole system and in a separate double-insulated box as it is part of TT earthing for the control panel, and serves to protect against cable damage on route to the PSU, etc.

TL;DR it needs a bit more context
many thanks

the earthing system is TN-S

the RCD is inside the control panel and has only the 230v/24v PSU connected to it

my other thought is the RCD nuisance trips and then the 24v d.c is lost. There are solenoid valves, pressure sensors etc in this design along with PLC control for such sensors.

I just do not see the reason the placing an RCD at this location (electrically speaking)

thanks
 

Reply to RCD before a 230v/24 PSU? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A recent thread was discussing having a delay RCD (type A or AC) for TT before a garage CU with a type B RCD for an EV charger. The question was...
Replies
25
Views
7K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
hope this helps Level 3 Certificate in Electrotechnical Technology Unit 2: Installation...
Replies
9
Views
7K
Martyc
M
A
Sample Questions C&G 2392-10 Certificate in Fundamental Inspection & Testing - paper 2 ( 1 ) The person who tests and signs the Electrical...
Replies
20
Views
27K
Deleted member 26818
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock