Discuss RCD both tripping and refusing to trip!? in the UK Electrical Forum area at ElectriciansForums.net

yep i didn't have time for three of the NE IR tests and hadn't thought through the rest. Am really grateful for the advice on testing between neutrals etc.

What's also on my mind is that the house seems to have been working fine. It was bought with no certification, I conducted initial testing and from then it didn't trip once.

its a basement and ground floor flat and yesterday I worked on the ground (and kitchen inclusive) floor in other rooms than the kitchen converting pendants to downlighters. I have been really careful to drill around the conductors and core out separate holes into which the conductors will be redirected. In all this I only saw one instance in which a bit of sheathing was scuffed but I guess I have to face the posibility that I missed something.

On the topic of the ceiling there was another thing that really worried me. It is plaster/fire proof board city plus ... three layers on the basis of lard and plaster. the thing that worried me, and counting down from the lard and plaster, was that there was a one cm gap between the first and second layers.

what advice or comments would you make to the owners?

So there is your starting point!
 
Yes and it seemed to be going well until today.

I just cant see how all four circuits on the one RCD (cooker and three power) can be affected when the only other circuits are lighting!? I've not seen evidence of a circuit crossover.

I also don't know how it is possible for an RCD not to trip when tested in one circumstance but to trip as expected in another. This is a burning question for me.

I will also fabricate a "circuit" from the RCD in situ test it in another way.

Is this a split board? Are there lighting circuits on both sides? If so turn off all lighting mcb's and try your rcd.
 
The only way forward it to assume every single cable on every circuit has been vandalised by persons unknown.
Not forgetting outside as well, e.g any excavations that may have damaged the incoming supply cable.

Start at the begining with all circuits disconnected, test the obvious ones first where you know there has been a problem, cut cables, exploding radios etc.
 
When I first returned to the job I tinkered with a lighting circuit
its a basement and ground floor flat and yesterday I worked on the ground (and kitchen inclusive) floor in other rooms than the kitchen converting pendants to downlighters
if you used jb to replace pendant and wire d/lights, check connections there (particularly if pendant was loop in/out) and perhaps check 2way from basement re borrowed neutral as stated in other replies (if feed @ switch)
just a thought if n-e tests don't help. also re-check ring continuity and figure of 8 and maybe socket that didn't like your choice of music.
 

Reply to RCD both tripping and refusing to trip!? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
791
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
884
Hi, while testing the new board I installed I got to the live testing at the sockets one of the RCD's kept tripping during the loop test, the...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock