Search for tools and product advice,

Discuss RCD disconnection times! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Hi all, just a quick one regarding RCD disconnection times.

So for non rcd protected circuits disconnection times of 0.4 / 5 seconds and 0.2 / 1 second for TN + TT final and distribution circuits.

RCDs (fire / fault protection) usually 300ms at rcd for rated current. (differs when s type).

So if I'm using an RCD in a TT system for fault protection due to high Zs readings am I to use the 300ms of the above OR use the 200ms for the TT?

And then what would I record on the test sheet as there's only one rcd test result box? Would it be the X1 for fault protection or the X5 for the additional protection? I think naturally I would put both down to prove both functions were operating in time.

I know it'll be a very simple answer but I'm just overlooking it. I don't have any books to hand at the minute as I'm out the country but it's one that just crossed my mind.

Thanks.
 
You mean you have gone away and did not take your OSG with you. ?

Lots of variables to take into account for a simple answer, BS number, circuit breaker type, rating and how high the Zs is?

Don't overthink this enjoy your holiday and just drink more.
 
You use 0.2sec. On the schedule you record ×5 for 30ma devices (the fact this is for additional protection isn't really relevant as the device will also provide fault protection), anything above 30ma you record ×1.
 
You mean you have gone away and did not take your OSG with you. ?

Lots of variables to take into account for a simple answer, BS number, circuit breaker type, rating and how high the Zs is?

Don't overthink this enjoy your holiday and just drink more.
Haha!

It was more just a simple example, so say I had a zs of 85 ohms, which is obviously too high for fault protection from a bs 60898.. So I'd use the 61008 of a split load board say to protect for fault current.

So if I got 250ms trip time for the 61008 at rated current would that be OK. I'm inclined to say it would as its below the recommended 300ms at rated current given in the table (forgot table number) but its just thrown me off a little with an mcb or non rcd protected circuit being 0.2s?

Im actually working on a vessel in Taiwan haha, I wish i was in holiday and drinking beer!! Cheers.
 
You use 0.2sec. On the schedule you record ×5 for 30ma devices (the fact this is for additional protection isn't really relevant as the device will also provide fault protection), anything above 30ma you record ×1.
That answers my question. Perfect thanks for that westward10!

Explains it all perfectly. I was just a bit q confused as it says 300ms for RCDs at rated current or 0.2 in TT systems.

Is that because its the lesser of the two figures (0.2 and 300ms?)

So a TN system is 0.4s but rated current of RCDs are 300ms.. Use the 300ms as its the lesser?

Thanks again
 
That question has made me see my fault.

I've got it from the rcd trip times. I was using the x1 figures of 300ms.

If an rcd was used for fault protection (for example 100ma at rated current would be 300ms trip time)?

So if I'm using 30ma RCDs regardless wether it's for fault or additional it would be x5 and 40ms.

If I was using anything other than 30ma it would be x1 and 0.4 for TN systems and 0.2 for TT systems?
 
A 30ma device to EN61008 or EN61009 should trip within 300ms at ×1. If these are being used for fault protection then they must disconnect within 200ms for TT. So regardless if for fault and/or additional a 30ma device should trip at 200ms or less for ×1 and 40ms or less for ×5. You will only record ×5 however as this is the prevalent measurement.
 
A 30ma device to EN61008 or EN61009 should trip within 300ms at ×1. If these are being used for fault protection then they must disconnect within 200ms for TT. So regardless if for fault and/or additional a 30ma device should trip at 200ms or less for ×1 and 40ms or less for ×5. You will only record ×5 however as this is the prevalent measurement.
Yeah, that's how I thought it was but went about explaining it the very long way. Thanks for your time. ?
 

Reply to RCD disconnection times! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Replies
3
Views
1K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
387
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
912
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
397

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top