Hi everyone,

I appreciate this is probably a really silly question.

I’ve come across the below test question and although I know how to find the answer, I don’t understand why we would need to know what the max permissible earth fault loop impedance is in relation to a 30mA RCD? I hope someone can offer some simple logic as to why we need to know this?

The question is:
Calculate max earth loop fault impedance permissible for a 30mA RCD used to protect a circuit on a TN-S supply

A. Nominal voltage / RCD trio rating = max earth fault loop impedance

Again, it’s just the theory of reason behind the question that I’m struggling with.

Thanks again as ever.
 
If the EFLI is too high, in the event of a fault the leakage might be less than 30mA and the RCD might not trip. Same as with OCPD but a much higher EFLI is tolerable due to the low current involved. However, FWIW if the EFLI is that high it is likely to be unstable, e.g. if due to Ra of an earth electrode. Therefore, the practical application of this limit is unlikely.
 

Reply to RCD impedance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top