Discuss RCD impedance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
8
Hi everyone,

I appreciate this is probably a really silly question.

I’ve come across the below test question and although I know how to find the answer, I don’t understand why we would need to know what the max permissible earth fault loop impedance is in relation to a 30mA RCD? I hope someone can offer some simple logic as to why we need to know this?

The question is:
Calculate max earth loop fault impedance permissible for a 30mA RCD used to protect a circuit on a TN-S supply

A. Nominal voltage / RCD trio rating = max earth fault loop impedance

Again, it’s just the theory of reason behind the question that I’m struggling with.

Thanks again as ever.
 
If the EFLI is too high, in the event of a fault the leakage might be less than 30mA and the RCD might not trip. Same as with OCPD but a much higher EFLI is tolerable due to the low current involved. However, FWIW if the EFLI is that high it is likely to be unstable, e.g. if due to Ra of an earth electrode. Therefore, the practical application of this limit is unlikely.
 

Reply to RCD impedance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi guys was having a conversation as a apprentice I’m still not sure and was wondering why earth fault loop impedance is important if you’ve...
Replies
9
Views
3K
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock