Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth RCD,s behave normally Ze .18 didn't clamp the earth to check any current flow did't think of it till on my way back, the only other thing I did after the tests was connect an outside light for the tenant to existing cable, so i am thinking a shared N any clues would be great
Dev
 
I think you have mis read my OP,

I don't think it's that the OP has been misread, than the fact you've explicitly stated you're going to be disconnecting CPCs with the assumption you will be re-energising (otherwise how would you be able to see that RCDs are behaving).

so my plan is to disconnect the earths one by one to get the RCD to behave and hopefully indentify the culprit
 
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
 
Like I said done that and all test come back ok, but, and this is the bit that aint playing ball with every circuit without anything plugged in, cooker,shower immerse etc etc all disconnected and all bulbs out and in the switched on position doing a global IR I get a X reconnected everything I get random trips, dis main earth random goes away
 
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
Thats because you assume I am some sort of idiot
 
Disconnecting a cpc when there is a known fault to earth could raise the earthed parts of that circuit (or if you disconnect the main earth, then all exposed and extraneous parts) up to the line voltage which is not a safe thing to do.
I would recommend that if your IR tests are coming back OK and you cannot find the fault by dead testing that you disconnect a circuit entirely (i.e. at least line and neutral) to remove it from the installation. Then if you put a high powered load on another circuit and the RCD does not trip you have disconnected the faulty circuit and can start checking that one in detail.

In this way if a faulty circuit is still present the RCD will limit the risk.
 
Mud slinging aside, if you've done the dead tests in the correct order, you should of discovered the fault before the live tests. Once on a rewire, I discovered a neutral earth fault on a radial and decided to put it to one side for later, to get the other circuits on. Except I didn't and mixed it up with another radial and connected it up. Got to RCD test and wouldn't function, neither would RCD test button. Went back to basics, and discovered my mistake.

Happy hunting:)
 
Have you got an earth clamp meter?

I think you need to check the residual earth loss across the installation and I suspect you have a combination of a N-E fault and cumulative earth leakage from plugged in devices....
 
A neutral earth fault can prevent the RCD test button tripping the RCD, see my and others previous posts. Don't ask me why, I'm not that clever, others might have the technical reason. From personal experience, but once experienced, its something you remember.
 
In the end it was a new LED hall light I put in before I took the old board out to give my self light to work as there was none there to begin with, I rigged it up from the henly blocks all kosher via a temp fcu,and it was the last thing into the board and this was causing the issue, as I said my plan was to remove the earths in turn till the tripping stopped and it was the culprit, what' the saying assume nothing suspect everything, well I assumed "cos its new it's ok" , all circuits test out great and as it is class 2 I disconnected the earth till scewjobs send a new one, cheers all for insisting I had a N..E fault
Pict
 

Reply to RCD issue, or is it? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top