Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss RCD issue, or is it? in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. the pict
    Offline

    the pict Forum Mentor

    Location:
    Brodick
    Business Name:
    Devlin Maguire Electrical
    Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth RCD,s behave normally Ze .18 didn't clamp the earth to check any current flow did't think of it till on my way back, the only other thing I did after the tests was connect an outside light for the tenant to existing cable, so i am thinking a shared N any clues would be great
    Dev
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    or a N-E fault.
     
    • Like Like x 2
  3. the pict
    Offline

    the pict Forum Mentor

    Location:
    Brodick
    Business Name:
    Devlin Maguire Electrical
    Yep most likely, going back any way to fit a shed light, so my plan is to disconnect the earths one by one to get the RCD to behave and hopefully indentify the culprit, is there anything else you can suggest may be contributing
     
  4. hightower
    Offline

    hightower Guest

    Unless I'm being a dipstick, shouldn't your plan revolve around proper testing rather than disconnecting conductors designed for safety? First place to begin is with an IR test....
     
    • Like Like x 3
  5. polo1
    Offline

    polo1 Electrician's Arms

    Location:
    Glasgow
    Business Name:
    GW Electrical & Security
    As Hightower has suggested, IR tests are the first step (assuming rcds are ramping ok and within specified tripping times).
    Please tell us you don't intend to leave cpcs disconnected:confused1:
     
    • Like Like x 2
  6. hightower
    Offline

    hightower Guest

    And to go one further than this, not only should you not be disconnecting CPCs whilst the installation is energised, your IR tests should be carried out with all CPCs connected to the busbar and all bonding in place.
     
  7. the pict
    Offline

    the pict Forum Mentor

    Location:
    Brodick
    Business Name:
    Devlin Maguire Electrical
    I think you have mis read my OP,
     
  8. hightower
    Offline

    hightower Guest

    I don't think it's that the OP has been misread, than the fact you've explicitly stated you're going to be disconnecting CPCs with the assumption you will be re-energising (otherwise how would you be able to see that RCDs are behaving).

     
    • Like Like x 2
  9. the pict
    Offline

    the pict Forum Mentor

    Location:
    Brodick
    Business Name:
    Devlin Maguire Electrical
    OK disconnect each circuit in turn,test RCD, if it behaves then the fault has been found
     
  10. DPG
    Offline

    DPG Respected Member

    Location:
    S Yorkshire
    What dead test results did you get?
     
  11. hightower
    Offline

    hightower Guest

    Or, and stick with me on this because it is a totally radical idea, you could plug in an IR tester and try and find the fault using the method every electrical book going would explain. You know, just a crazy thought?
     
    • Like Like x 1
  12. Rob
    Offline

    Rob Respected Member

    Location:
    North west
    An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

    As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
     
    • Like Like x 1
  13. the pict
    Offline

    the pict Forum Mentor

    Location:
    Brodick
    Business Name:
    Devlin Maguire Electrical
    Like I said done that and all test come back ok, but, and this is the bit that aint playing ball with every circuit without anything plugged in, cooker,shower immerse etc etc all disconnected and all bulbs out and in the switched on position doing a global IR I get a X reconnected everything I get random trips, dis main earth random goes away
     
  14. the pict
    Offline

    the pict Forum Mentor

    Location:
    Brodick
    Business Name:
    Devlin Maguire Electrical
    Thats because you assume I am some sort of idiot
     
  15. polo1
    Offline

    polo1 Electrician's Arms

    Location:
    Glasgow
    Business Name:
    GW Electrical & Security
    Sorry if I have! It did seem a bit strange:blush:
     
Loading...
Similar Threads - issue Forum Date
Electric fire circuit issue Electrical Wiring, Theories and Regulations Monday at 12:54 AM
Strange issue with drill Electrical Forum Thursday at 9:58 AM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job