Discuss RCD Keeps tripping and not mcb and not on the same side as MCB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Peter

-
Reaction score
0
Hello hoping someone can urgently help with an issue I am having.

I am carrying out electrical works on a 2 bedroom flat that is being refurbished. All I have done is changed single sockets to double sockets. Taken away a socket that was spured off another socket. Moved some lights into the middle of the ceiling and moved 2 light switches.

I am also not sure if the fault was already there or not but everytime I plugged in something that draws a fair amount of power I.e heater or grinder it would trip the rcd. I thought it may be an rcd fault so I moved the mcb to the other rcd and changed the rcd I thought was faulty. Now what is happening is when you plug something in that draws power it stays on but still trips the same rcd that I changed even though the mcb is not on that rcd side ?

What could this be ?
 
Likely to be a neutral-earth fault on a circuit on the side with the RCD that trips. Check the IR on all these circuits - it might have been pre-existing. The heavier the load, the more likely the trip, and it will happen regardless of which circuit the load is on.
 
But...

a) The problem was there before he changed anything in the board.
b) The circuit he moved now works, and doesn't trip its own RCD.
c) It trips mainly with heavy loads.

All three factors point at an N-E fault on any of the circuits on the RCD that trips, not necessarily the one that is loaded or the one he moved.

Sometimes I wonder if I'm the only person who actually reads the fault description before replying!
 
Hi - yep I'm going for the N-E fault too - and I raise that it's in one of the 1G to 2G outlet conversions you've just done (trapped N or some such) :) .
 
Hello hoping someone can urgently help with an issue I am having.

I am carrying out electrical works on a 2 bedroom flat that is being refurbished. All I have done is changed single sockets to double sockets. Taken away a socket that was spured off another socket. Moved some lights into the middle of the ceiling and moved 2 light switches.

I am also not sure if the fault was already there or not but everytime I plugged in something that draws a fair amount of power I.e heater or grinder it would trip the rcd. I thought it may be an rcd fault so I moved the mcb to the other rcd and changed the rcd I thought was faulty. Now what is happening is when you plug something in that draws power it stays on but still trips the same rcd that I changed even though the mcb is not on that rcd side ?

What could this be ?
Did you move the neutral to the other neutral terminal block?
as this would be the reason that the other RCD could be tripping out
I think that the reason the RCD tripped out in the first place would probably due to a neutral to earth fault, if this is so you want to move circuit back (together with neutral) I can't see your profile so I hope that this is a DIY job and not a paid job if so there has been no mention of testing.
 
Hello hoping someone can urgently help with an issue I am having.

I am carrying out electrical works on a 2 bedroom flat that is being refurbished. All I have done is changed single sockets to double sockets. Taken away a socket that was spured off another socket. Moved some lights into the middle of the ceiling and moved 2 light switches.

I am also not sure if the fault was already there or not but everytime I plugged in something that draws a fair amount of power I.e heater or grinder it would trip the rcd. I thought it may be an rcd fault so I moved the mcb to the other rcd and changed the rcd I thought was faulty. Now what is happening is when you plug something in that draws power it stays on but still trips the same rcd that I changed even though the mcb is not on that rcd side ?

What could this be ?
Hello mate. Any idea as to the construction of this 2 bed flat? Would you know if the ceiling is suspended and fixed to tin hat?
 

Reply to RCD Keeps tripping and not mcb and not on the same side as MCB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
570
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
485

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock