Discuss RCD Keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
I have recently added two double sockets in a lounge original nor realising that the source was a spur that someone had already wrongly spure, so two existing double sockets a spur from a spur I then added 2 sockets across the room on a back to back wall essentially creating 4 spurs which obviously tripped the RCB.After realising the mistake I added a 13A fuse before the first socket to prevent tripping and make the original sockets safer also so the order now goes spured power into 13A fused split to feet 2 sockets that in turn feed 1 double socket each. Unfortunately the problem has persisted I have tested all sockets with a fault plug and all register correctly wiring and no faults. I don't know if this is earth leakage from an appliance or RCB failure the main CU only has 2 RCBs one for lights and one for the entire ring Main B32 30mamp load and another B6 for the lights and 1 MCB each which seems minimal
 
I have recently added two double sockets in a lounge original nor realising that the source was a spur that someone had already wrongly spure, so two existing double sockets a spur from a spur I then added 2 sockets across the room on a back to back wall essentially creating 4 spurs which obviously tripped the RCB.
Too many spurs is more of a fire hazard as you can draw enough current to exceed the max limit of the cable. Typically your over-current protection is a 32A MCB but a ring final circuit (RFC) is wired in 2.5mm cable which is typically rated to around 20A (depends on installation method = thermal resistance) but safe for the RFC as there are normally two "legs" sharing the current to a reasonable degree.

If you have more than one spurred off a RFC you should have it from a 13A fuse connection unit (FCU) as you have done for this reason (basically treating it as a hard-wired extension lead).

A lack of that protective fuse would not trip a RCD.
After realising the mistake I added a 13A fuse before the first socket to prevent tripping and make the original sockets safer also so the order now goes spured power into 13A fused split to feet 2 sockets that in turn feed 1 double socket each. Unfortunately the problem has persisted I have tested all sockets with a fault plug and all register correctly wiring and no faults. I don't know if this is earth leakage from an appliance or RCB failure the main CU only has 2 RCBs one for lights and one for the entire ring Main B32 30mamp load and another B6 for the lights and 1 MCB each which seems minimal
Realistically you would be best to get a professional electrician in to check it out.

They would have the tools to test the cable insulation at high voltage for faults, and also usually to actually measure the leakage current and the trip threshold of the RCD to see if it is something "hard" like a damaged cable (N-E faults are often the trickiest to track down as L-E normally goes with a BANG!), or "soft" such as too much electronics plugged in to on the same circuit, all adding up the odd 0.5-2.0mA here and there, until you are close to the RCD's threshold.
 
A spur from a spur wouldn’t trip an rcd.

an rcd or rcbo looks for an earth fault whereas an mcb looks for overload. (Nothing actually plugged in, no load)

you’ve done right by creating a fused spur, and by limiting the supply to 13A.

if the rcd trip is constant, check for a squashed cable behind a socket.
 
Too many spurs is more of a fire hazard as you can draw enough current to exceed the max limit of the cable. Often your over-current protection is typically a 32A MCB but a ring final circuit is wired in 2.5mm which is typically rated to around 20A (depends on installation method = thermal resistance) but safe for the RFC as there are normally two "legs" sharing the current to a reasonable degree.

If you have more than one spurred off a RFC you should have it from a 13A fuse as you have done for this reason (basically treating it as a hard-wired extension lead).

A lack of that protective fuse would not trip a RCD.

Realistically you would be best to get a professional electrician in to check it out.

They would have the tools to test the cable insulation at high voltage for faults, and also usually to actually measure the leakage current and the trip threshold of the RCD to see if it is something "hard" like a damaged cable (N-E faults are often the trickiest to track down as L-E normally goes with a BANG!), or "soft" such as too much electronics plugged in to on the same circuit, all adding up the odd 0.5-2.0mA here and there, until you are close to the RCD's threshold.
Would splitting the ring main onto more CBOs prevent th
Could be a nick on cable which is just touching the back box or a cable caught by the faceplate screws.
What is the best way to trouble shoot that as I'm guessing it would be to go over all the new connections in turn also this happens every 4 to 6 hours or more sometimes with heavy load items ie kettles etc also happens under low load in the night
 
Would splitting the ring main onto more CBOs prevent th

What is the best way to trouble shoot that as I'm guessing it would be to go over all the new connections in turn also this happens every 4 to 6 hours or more sometimes with heavy load items ie kettles etc also happens under low load in the night
In what part of Liverpool are you, I'm out and about tomorrow so I may be not to far from you
 

Reply to RCD Keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
612
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
810
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
302

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock