What is the best way to trouble shoot
Bearing in mind your level of experience I would advise you go back over all the electrical accessories you have connected, with particular attention paid to those secured to metal back boxes (as suggested in a previous post). If that fails to find it, I would suggest you get in a professional (as suggested in a previous post)
 
Would splitting the ring main onto more CBOs prevent th

What is the best way to trouble shoot that as I'm guessing it would be to go over all the new connections in turn also this happens every 4 to 6 hours or more sometimes with heavy load items ie kettles etc also happens under low load in the night

Have you taken N to E resistance with the mains/RCD switched out?.
 
Are we sure that it's an RCD that's tripping and not a circuit breaker. If it takes a few hours to trip, it could be due to the circuit being overloaded. Maybe...
 
If it is a N to E fault then you could expect this to show up as the current flow through a (the) neutral is increasing as there normally is only a volt drop or so with low flows which then increases with increasing current flows but even if there is only say 1 volt in the neutral cable at the fault location; a fault resistance of ~ 33 ohms will have no bother in tripping the RCD, a simple N to E resistance test with a multimeter could easily pick this up, if no fault the resistance will be infinity.
 
If it is a N to E fault then you could expect this to show up as the current flow through a (the) neutral is increasing as there normally is only a volt drop or so with low flows which then increases with increasing current flows but even if there is only say 1 volt in the neutral cable at the fault location; a fault resistance of ~ 33 ohms will have no bother in tripping the RCD, a simple N to E resistance test with a multimeter could easily pick this up, if no fault the resistance will be infinity.
I've had purchases an advanced kewtech plug tester that tests the loop and continuity also. Last night we turned off the power to the fused spur/s and it was still tripping does this mean that the fault has to be elsewhere? I am guessing at moisture or water in the outside sockets after this heavy rain etc!
 

Reply to RCD Keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
612
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
808
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
301

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock