Discuss RCD Not tripping when in contact with live conductor in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi All
Please correct me if I'm wrong I was thought that an RCD should trip when you come In contact with a live conductor. Now I have had 2 electric shocks in the last 3 months and on both occasions and the RCD did not trip.The RCD was tested and passed.
Any ideas ?
 
Idea 1: learn safe isolation!!
 
The answer is obvious.

2 shocks in 3 months, you're not learning fast enough but you're also not dead.

The current passing thro' you was less than the RCD tripping current (assuming the RCD is working O.K)

Been there, done that, as have most people.
 
Guys is the Op an electrician or a member of the public though, The username doesn't strike me has a sparks username.
I may be wrong it does happen!. OP can you confirm who/what you are??
 
Iirc this is not an electrician. Lillyrose had a problem that a lot of people were advising on hence the fairly high post count.
On the other hand it could be a spark who likes flowers :)
 
He might not be a spark and he also might not be working on his house he might just be getting a shock from a metal switch or something, if you are not a spark then please get some one out to check your electrics to make sure they are safe. If you are a spark make sure you safely isolate before you work on it.

What milliamp is the rcd it may be the wrong one.
 
Last edited:
Hi All
Please correct me if I'm wrong I was thought that an RCD should trip when you come In contact with a live conductor. Now I have had 2 electric shocks in the last 3 months and on both occasions and the RCD did not trip.The RCD was tested and passed.
Any ideas ?
Two things spring to mind, firstly the RCD is rated to trip at 30 mA usually will give you a bigger shock than most people imagine. Even if a 15 mA fault current flows through you you'll know about it in no uncertain terms. Secondly if you were tinkering inside an appliance or electrical fixture and you got a shock from the live whilst you were also in contact with the neutral then the RCD won't detect this as a fault and won't trip regardless of how big a shock you get.

As previously mentioned, learn to isolate things before sticking your fingers in. You might not be so lucky the next time.
 
30 mA usually will give you a bigger shock than most people imagine
Indeed. For comparison, I can detect about 1/4 mA (250µA) by stroking the live surface with knuckles, feel 1-2mA with fingertips, and would consider 5mA a definite shock under average conditions. 30mA is a practical compromise between safety and unacceptable nuisance tripping. On 120V systems in the USA where typical leakage currents are lower, GFCI's are usually rated to trip (albeit slowly) at 6mA. I build portable electronic equipment with unavoidably high leakage currents, often 1-2mA, approaching the safe limit to run from a plug and socket outlet without a high-integrity CPC. When the tangle of extension leads gets mashed and the CPC broken, I usually get a call asking why they are getting shocks off my equipment without anything tripping...
 
Two things spring to mind, firstly the RCD is rated to trip at 30 mA usually will give you a bigger shock than most people imagine. Even if a 15 mA fault current flows through you you'll know about it in no uncertain terms. Secondly if you were tinkering inside an appliance or electrical fixture and you got a shock from the live whilst you were also in contact with the neutral then the RCD won't detect this as a fault and won't trip regardless of how big a shock you get.

As previously mentioned, learn to isolate things before sticking your fingers in. You might not be so lucky the next time.
I don't think the tripping current has been mentioned. Might even be an old ELCB
 

Reply to RCD Not tripping when in contact with live conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
908
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
605
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock