Hi all,

I have been asked to install 2 x 32amp 3 phase sockets, one is to be used to plug in a forklift charger, the other one they are not yet sure but want one available for the future. What are people's thoughts on the omission of RCD's in what circumstance would a risk assessment negate the need for an RCD protected socket ? Is it only if the outlet is to used by an electrically skilled person?

Thanks,
 
Personally I would only be happy to omit RCD for technical reasons, such as the nature of the load and usage means RCD nuisance trips are likely and/or have serious impact on safety or business continuity.

As @freddo says the socket/RCD outlets are probably the easiest and most cost-effective solution as 3-phase RCBO are costly, not always available, and/or take a lot of space in the DB as a MCB add-on unit.

Also may places keep the DB locked for good reasons, at least with the RCD at the socket if it does trip it is easy for the operator to reset it.
 
Hi all,

I have been asked to install 2 x 32amp 3 phase sockets, one is to be used to plug in a forklift charger, the other one they are not yet sure but want one available for the future. What are people's thoughts on the omission of RCD's in what circumstance would a risk assessment negate the need for an RCD protected socket ? Is it only if the outlet is to used by an electrically skilled person?

Thanks,
Why do you feel you need to omit the RCD?
 
The cost of RCD add on modules for 3ph stuff is usually very high,, as well as taking up lots of extra ways in the db, so we mostly fit 3 phase switch interlocked sockets that have a built in RCD.
Just had a quote for Hager ones and they are £165 ?
 
Just had a quote for Hager ones and they are £165 ?
I ended up using MCB in the DB and putting some 3-phase RCD, and double-pole single phase RCD, in an additional DIN enclosure as better/cheaper than some of the RCBO options I was quoted. I also needed the DIN rail box for other stuff so the cost & time to put it in was only different by going 4-row instead of 2-row.
 
I ended up using MCB in the DB and putting some 3-phase RCD, and double-pole single phase RCD, in an additional DIN enclosure as better/cheaper than some of the RCBO options I was quoted. I also needed the DIN rail box for other stuff so the cost & time to put it in was only different by going 4-row instead of 2-row.
I find myself doing this instead of the RCBOs as well. Some of the prices are just ridiculous
 

Reply to RCD omission in a commercial setting. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
842
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock