Discuss RCD or Not in the UK Electrical Forum area at ElectriciansForums.net

S

simonspark

Evening All,
Could one of you fine tradesmen, there's got to be one out there, help me out a bit here. I have been asked to install a ring circuit that is going to supply 17 computers in a school. I know that its going to be an IT install (separate earth terminals and all that) but what about the RCD situation? The regs state that the sockets should be protected by an RCD. But the natural leakage could well trip an RCD. I could split the circuit into two or more rings, but the logistics of doing such a thing are staggering. Trust me! Can I just put labels on each socket stating that they are for IT equipment only? And all wiring is going to be surface (nice!)
I am going to have to thankyou in advance, because the last time I tried such an action I failed.
Thanks
 
ok........ could you not run radials for these circuits? 2x 4mm Radials and run a 4mm Earth with each to comply with 543.7.1.2
i Would do 2 circuits and have 8 pcs and 9pcs per circuit. Protected by a 30mA RCBO.
 
Correct but 3.5 is probably slightly higher than what you will actually get i have seen installations designed for 7 pcs happily living with 10pcs. You can make it 3 circuits if you prefer.
 
And now I have to install 3 x 4mm twin and earths complete with 3 x 4mm single earths. And you should see all the data trunking that needs to be bridged! And the 18 way cu is full! And I cant lift the floors and the cornice is a decorative bugger about 18 inches down and the same across.
 
I am qualified, 99.4 % on the 17th Easy exam (one wrong!!). And have done the amendment 2011. I am looking for an answer or should I say a get out clause where the works can be done without costing 2K! 2 million pound liability
 
If it is acceptable to mark up a non RCD protected socket with a label stating fridge/freezer only (taking into account of no flush wiring) why is it not the same for IT equipment.
 
The first thing you need to do is check with the Local Authority (assuming the installation is under their control) to see if there is a published specification covering this issue.

The last school installation that we did had a 'mini spec' stipulating RCD protection, high integrity earthing and a maximum of 6 'terminals' per ring final circuit.
 

Reply to RCD or Not in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
345
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
823
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
257
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
804
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
307

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock