I would split the ring as Murdoch has outlined and then put into practice what Handy sparks has said re switching over to low ohms which will start to narrow it down and get you closer to the problem.

Before you split he ring test end to end continuity first on all your cables.

Good luck!
 
I had a similar problem just before Christmas...is the central heating on the circuit? if so check that the pipe monkey hasnt terminated into the feed side for the boiler wiring. I had a CH pump go faulty, switched everything off, unplugged everything and after a short while of halving the circuit, i checked behind the FCU to discover they had terminated to the feed, not load. Try that for all FCUs. Drop all socket faces too before breaking down circuit in case someone has terminated a light point, shed, garage into the back of a socket. Good luck
 
Remember even although you have the switch off the socket and the FCU both could be single pole switching I spent ages trying to find a fault and tracked it down to the electric fire had a neutral to earth fault fed from a SP FCU also you say that everthing was unplugged but never take it for granted as some clown could have spurred off to feed say a outside light
 
Remember even although you have the switch off the socket and the FCU both could be single pole switching I spent ages trying to find a fault and tracked it down to the electric fire had a neutral to earth fault fed from a SP FCU also you say that everthing was unplugged but never take it for granted as some clown could have spurred off to feed say a outside light

or even wired in a spurred socket under the floor on the landing and plugged a signal booster in. Seen it.
 
Found the issue!!!

The kitchen sockets were run as spurs from spurs from spurs etc!! it turns out the feed from the kitchen comes from one socket upstairs that then went into a JB in the ceiling of the kitchen Extension and then splits into 2 radials. None of the cables fused down. There was a leak in the roof of the extension which was causing the JB to get wet thus giving me the fruity readings and tripping the RCD

I ended up Isolating the circuit from the socket which cleared the fault. The Oven and Hob are fed from different circuits each with their own isolator and socket and there is a computer socket in the kitchen that is on another circuit not on the RCD side of the board. so she still has some power in the kitchen that she can plug fridge into etc. I have advised my sister that the house needs a rewire to get rid of all the dodgy circuits but she cant afford one right now so things will stay as they are.

Thanks for all your help guys!

Dave
 
Last edited:

Reply to RCD Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
512
Hi Basically I have visited a youtube link of another electrician and he is talking about how many electricians find RCD fault very hard to...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock