Discuss RCD protection in garage in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
If I have a distribution circuit (to a garage with accommodation upstairs) does the CU in the garage have to have RCD protection or is it sufficient for the main CU in the house that feeds the garage to have RCD protection? Just wondering about regulation 411.3.3 additional protection as there will be sockets and a shower in the garage.

Thanks for any replies

D2E
 
It could be either.

Have a little think about why we need rcd protection and not just for sockets etc.

It can depend on the installation method.


Sent from my iPhone using Tapatalk
 
Is the garage a TT conversion if so all circuits will require RCD protection.
One question what sort of loading will the garage have a shower sockets and lighting may be a bit too much to supply from a spare way in the main CU.
All circuits in a room containing a bath or shower require additional protection.
 
If I have a distribution circuit (to a garage with accommodation upstairs) does the CU in the garage have to have RCD protection or is it sufficient for the main CU in the house that feeds the garage to have RCD protection? Just wondering about regulation 411.3.3 additional protection as there will be sockets and a shower in the garage.

Thanks for any replies

D2E

You say accommodation upstairs. Is it for a member of your family or a lodger/rental? If so, they will not want to be knocking on your door to reset an RCD.
 

Reply to RCD protection in garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
746
HI folks, I'm on the management committee of the block of flats where I live. We've got ancient garage electrics and want to rewire. I have a...
Replies
4
Views
813

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock