Discuss rcd protection on sockets in the UK Electrical Forum area at ElectriciansForums.net

If you are worried about nuisance tripping, if practically possible, why not split the radial into 2 or 3 circuits rather than one? As Lucien mentioned, if the accumulative earth leakage is sufficient to trip the rcd then it could be dangerously high anyhow, potentially making the circuit unsafe to use. Omitting the rcd rather than re-designing the install is not the answer. It is your duty as an electrician to design any install to a safe standard for all possible scenarios.

You cannot rely on a person's "word" that nothing else will ever be plugged in. You know as well as I do that this just doesn't happen in real life.

I think you are doing the right thing by installing a rcbo
i did consider extra circuits but not enough room in board
 
Lack of space in the CU isn't an excuse. The circuit can be surface wired from a non RCD protected spare way in the CU to more than one RCD FCUs close to the sockets, with each RCD feeding a group of sockets.
 

Reply to rcd protection on sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
983
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
281
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
899
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
545
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock