Currently reading:
RCD protection

Discuss RCD protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
hi all

conducting eicrs in amusement arcades usually nothing is RCD protected.

sockets no RCD protection in general is c3 but when would this become c2 in this instance as it is an existing installation decades old
 
i might be inclined to give it a C2 ifused for portable appliances, e.g. vacuum cleaners.( you know how thick cleaners can be ). otherwise a C3.
 
What if accessible to public/ ordinary persons
You have to assess the risk on site, we can't do that for you.

If sockets are positioned for gaming machines with little or no access then C3. General use sockets for use by staff potentially a C2 but can be swapped out for point of use RCD socket-outlets.

If pointed at with a big flashing arrow saying "free electricity here" then C2.
 
Your report - your decision on the severity of the non-compliance. But it must be coded.
Ok.... I’m looking for a more direct actual guide on this it’s not as black and white as you say ofcourse it is to be coded and I don’t agree it’s just the inspectors decision as there is a correct way to inspect and code.
are we going on the basis that all sockets to be RCD protected upto 32a during a eicr even though the installation is compliant to older regulations without RCD protection
 
Unless there is a risk to life and property etc then you can only recommend upgrading to current standards, you cannot use coding to force customers to upgrade.
 
Ok.... I’m looking for a more direct actual guide on this it’s not as black and white as you say ofcourse it is to be coded and I don’t agree it’s just the inspectors decision as there is a correct way to inspect and code.
are we going on the basis that all sockets to be RCD protected upto 32a during a eicr even though the installation is compliant to older regulations without RCD protection
It is the inspectors decision. There is no hard fast rules on how to Code, this is the only area BS7671 makes a Coding reference to, that being a minimum Code 3. This is not suggesting if must be Code 3 because this is down to the inspectors judgement and experience.
 
It is the inspectors decision. There is no hard fast rules on how to Code, this is the only area BS7671 makes a Coding reference to, that being a minimum Code 3. This is not suggesting if must be Code 3 because this is down to the inspectors judgement and experience.
Don’t agree with that , if it’s a situation that warrants RCD protection the inspector can’t just say c3 and that’s the end of because he decided , if the inspector is wrong he is wrong and his coding would be wrong also
 
Don’t agree with that , if it’s a situation that warrants RCD protection the inspector can’t just say c3 and that’s the end of because he decided , if the inspector is wrong he is wrong and his coding would be wrong also
Whether you agree or not that is the way of things. Are you new to doing this kind of thing.
 
No not new been doing it for years , just a grey area to me of when we should class no RCD to sockets a c2 when it’s a building that’s older and open to public
The age of an installation isn't overly relevant. Code 3 would be a statement of fact that socket outlets do not have additional rcd protection, a recommendation of improvement. Code 2 you are implying a situation warranting urgent attention, if you can justify this with evidence that such a situation is pending then that is acceptable.
 
The age of an installation isn't overly relevant. Code 3 would be a statement of fact that socket outlets do not have additional rcd protection, a recommendation of improvement. Code 2 you are implying a situation warranting urgent attention, if you can justify this with evidence that such a situation is pending then that is acceptable.
So the situation where historically no RCD protection has ever been in place say a 30 year old install and we now have public accessing socket outlets for use and for use of machines plugged into the sockets would that not require RCD protection
 
The fact public have access again is not really relevant they are no different to employed staff they all share the same risk.
 
So the situation where historically no RCD protection has ever been in place say a 30 year old install and we now have public accessing socket outlets for use and for use of machines plugged into the sockets would that not require RCD protection

Historical requirements are irrelevant, you carry out the report to the current version of bs7671.

As such General purpose socket outlets without RCD protection would be coded a minimum C3, however if the lack of RCD protection is considered to be potentially dangerous then a C2 would be appropriate.

If the sockets in question are supplying power to fixed, or not easily movable, equipment such as amusements, are not readily accessible etc etc then I would suggest that maybe they wouldn't need RCD protection at all. And then following suitable assessment of the risks no code may be necessary.
 
Gavin, all you can do is assess whether or not, how likely there is and the severity of a potential danger. The guide to coding hints on this (see post 25#) by indicating what type and use of equipment warrants how you code it. Its your call to determine the potential danger. If you feel certain sockets in the installation warrant a C2 then you code them accordingly otherwise the rest would be a C3.
You can then advise the client to what is the best method of rectification should this be required.
 

Reply to RCD protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top