Search the forum,

Discuss RCD question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

bs7671

Hi people can anyone tell me the difference between the tripping currents and the current ratings of rcds.Any help I would be thankful of
 
Tripping currents are the Ma rating you see on the RCD ie a 63a 30Ma. (Milli-amps)

This means under fault conditions the RCD will trip with only a 30Ma fault. As a fault can develop many 100's of amps very quickly under fault conditions you can see that 0.003amps is a very small amount and therefore will trip quickly.

Which is why when we test a RCD the normal tests are carried out in Ms (Milli-seconds) to see the trip times rather than the amount of Ma taken. There is a Ma test called a "ramp" test for Ma but that is another story.

The current rating is the 63a 30Ma part.

This is the rating for the circuit or cable load in amps. The circuit design and cable loading which is worked out in the design stage. So an example is a lighting cicuit in your home is most liklely 6 or 10 amps. That takes into account the number of lights which is the load and therefore the cable used.

The 6 or 10 amps protects the cable from damage. So you lighting RCD would be 6a or 10a 30Ma
 
I do have another question regarding r1+r2 testing.Would cross connecting line to cpc prove there are no parrellel paths and no earth faults.How exactly is it done?
 
It would not prove there are no parallel paths, it proves continuity of the protective conductor and the line conductor, and polarity. The circuit being tested has the CPC and line conductor connected together (de-energised first) and futherest point / highest reading gives you your R1 + R2 for the circuit.

Parallel paths are from incoming sevices (gas, water, et al) lowering the overall Ze, thats why these protective conductors are to be removed (de-energised first) before a Ze test.
 
Last edited by a moderator:
As this will become part of your course then the R1 + R2 will be done as a precursor to getting your Zs, as in Zs = Ze + ( R1 + R2).

In the real world the 17th edition meters will give you the Zs on a final circuit, etc by measurement. The measurement results will invariably be lower than if you did the test by calculation as that is when you get those parallel paths. Most electricians do the measurement method, though the NICEIC advise that Zs should be done by calculation as it's a live test, but that is another thing

If you left the Earth connected to the earth bar and then did the loop method you would get parrellel paths, off the commoned earths from other circuits and all your bonding. On new installations a lot of testing for initial verification is done before the connection to the CU as you will want to prove polarity at this point. On a PIR it can be slighlty different.

So with earth connected to Earth bar parallel earths, disconnected no parrallel earths

Only an insulation resistance test will pick up a fault, the cross over test will prove polarity
 
Remember that polarity is confirmed first in your "dead tests" CPC CRFC, and then again when the installation is energised to confirm the polarity is correct on the incoming supply.
 
Last edited by a moderator:
You are a wealth of electrical knowledge!I am trying to get my head around some of this and have found this forum one of the best resources.Educated people are willing to help us newbies by sharing their understanding and I think its great.I have got hundreds of questions and one day hope to be in your shoes sharing my expert advise.Thanks very much again
 
On any circuit that is part of the RCD, plug in the RCD tester and test @ 1/2 times there should be no trip within 2 seconds, test again @ 1 x and the RCD should trip within 200ms and again on the 5x setting (additional protection) the RCD should then trip within 40ms. Then press the test button on the RCD lastly.
This test should but never is repeated by the owner of the installation every three months.

All these tests should be conducted @ 0 and 180 degrees setting of the RCD tester and the highest figure recorded.

(All other tests should be exectued first as RCD testing is one of the last tests to be conducted on circuits).
 
Last edited by a moderator:
Thank you again. The best part to all this that people like antimatter and others here on the forum enjoy passing on this experience.

I had guys like them to ask on site when I did my apprenticeship many moons ago. The Pee take was horrendous but they like antimatter wanted to help and enjoyed it. The tradegy to this is that my generation don't have the chance to pass on this to new comers apart from the forums. Apprenticeships are trying to make a comeback, but without an industry in the UK where do they serve them??

Long may this and other forums exist to pass on that experience and help guys who like you seem to want to learn and improve their knowledge, as long as you keep asking people on here will keep helping, after all your going to be us ole F..ts one day lol
 
How do you carry out live testing of a single phase rcd?

Connect your tester as follows,
earth lead to earth bar in CU
Live lead to live load side of RCD, Neutral lead to neutral load side of RCD, press the test button and await. 7 tests are required to live test RCD.

x 0.5 of rated trip current
x1
and x5, all at zero degrees, then repeat at 180 degrees, then test mechanical function of test button.

Job done.

If it is easier you could also test the RCd at a suitable socket using the plug in lead that comes with your test set, i prefer to test at source.

Cheers........Howard
 
Last edited by a moderator:
Functional test ?;)

Are we going to also tell the lad about 100ma + rcd that only have the 1 and 5 times tests or about S type lol ............naw leave that for another day eh guys

We could go on forever, but i was just (like an earlier post) explaining the test procedure for the majority of RCD's found in 17th edition boards in domestic installs in the UK.

Cheers..........Howard
 
have to disagree with part of your answer, malcolmsandford. the rating in A e.g. 63A is the max.design load of the RCD, it's the MCB that is 6A or 10A. but your trip part of the answer was spot on
 
Yes if you were working on a split board Telectrix agree as you would have the mcb for overload protection and that 63amp RCD would be covering them.

I used the lighting example for a 6 or 10 amp RCD to be honest. I could have used something that took a 63amp supply. But off the top of my head could not think of anything domestically that would use that much lol. Could have gone into something commercial but then you might be pushed to find something single phase taking that much.

It was just to explain the use of the RCD, sorry for any confusion
 
Where abouts can I find a comprehesive list of all lables i.e danger ident and other notices according to the regs.Thanks guys
 
Well the onsite guide has a few pages and there is some stuff in bs7671 about where they go and why.I was after a kind of list of types a little less wordy,I mean its pretty obvious why we have them and where they need to go isn't it?
 

Reply to RCD question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
717
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
385
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
417
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
895
Hi, I am currently reading through the standard IEC 61439-1 - Low-voltage swtichgear and controlgear assemblies - Part 1: General rules, and on...
Replies
0
Views
129

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top