Discuss RCD refuses to switch on (up) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
-1
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
 
Firstly I hope you know what you are doing and can carry out safe isolation?

Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
 
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.
 
Can you post a photo of the RCD/board please?
 
I worked for years in electrical wholesalers and understand matters fine.
I reckon I do have a fault, however I cannot understand where. I tripped the in-house mcb and then disconnected the RCD, now when switched up it stays up.
Surely this means the fault is between the cu and the RCD, as I have thought until now, it’s simply a single length of cable within plastic conduit, even through the wall and right into the RCD! Thanks.
 
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
I had a customer did what the op tried to do ,he came of worse in the end .
 
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.

There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
 
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
Sorry misunderstood your description, my error
 
Can you post a photo of the RCD/board please?

Attached.

AEE57615-3C2B-44CE-B0A1-13640BD28C04.jpeg
 
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
What you describe as an ELCB what make and type is it
 
Firstly I hope you know what you are doing and can carry out safe isolation?

Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
As per my previous post; have you tried that?
yes, I replied above. The RCD stays on. I then reconnected the brown wire and it stayed on. As soon as I tried to connect the neutral the RCD tripped.
 
I'm beginning to think the N is connected to the wrong busbar in the house, I'm confused with the OPs description of how it is wired I have asked if he can post a pic of the house CU internals, just to be sure in my mind, hopefully he will.
 

Reply to RCD refuses to switch on (up) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
793
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
215
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock