Discuss RCD sockets regulation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it applies to all socket outlets, we have to install a 63A 5 pin socket located outside. Thanks in advance
 
411.3.3 30mA RCD shall be provided for socket outlets not exceeding 32 amps - for use by persons of capability BA1, BA2, or children; and in other locations; and for mobile equipment to be used outdoors.

But see note 3 - RCD protection for all socket outlets is recommended.
 
I'm told it applies to all socket outlets,

Told by who?
If you are being told this by the person who is paying you then crack on and do what they want.
If you are being told this by someone else then ignore them.

You are right that it is sockets of 32A or less which require additional protection by 30mA RCD (RCD protection may be required for other reasons such as fault protection in a TT system)

You might decide that, above and beyond tbe requirements of the regulations, 30mA RCD protection is beneficial for your particular application, but it is not a requirement.
 
Told by who?
If you are being told this by the person who is paying you then crack on and do what they want.
If you are being told this by someone else then ignore them.

You are right that it is sockets of 32A or less which require additional protection by 30mA RCD (RCD protection may be required for other reasons such as fault protection in a TT system)

You might decide that, above and beyond tbe requirements of the regulations, 30mA RCD protection is beneficial for your particular application, but it is not a requirement.
Thank you Dave , the reason I asked was that I was told it had been amended but couldn't find it so I was sceptical anyway.
 
Thank you Dave , the reason I asked was that I was told it had been amended but couldn't find it so I was sceptical anyway.
The main amendment change was that the omission of RCD protection now requires both a risk assessment and to be in use only by skilled/instructed personnel.

An example of where that is an appropriate approach is a computer room where you might have racks equipment with lots of leakage fed from 16A or 32A connectors. The room is normally secured and only staff in there would be technically qualified, also it is usually a clean, dry, and well organised/tested so the risk of a shock is low as well.
 

Reply to RCD sockets regulation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
352
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
205
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock