Discuss RCD Testing Confusion - Help! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
-1
Hi

Ive got a question regarding RCD tests.

If a DB had 7-8 ccts on MCBs all covered by a Main RCD, should we do only one cover-all test on the main RCD, or record an individual RCD test for each circuit?

Other sparkys on my firm have been doing an RCD test for each circuit, effectively testing the same RCD 8 times.

What is the correct procedure?

Thanks
 
you test the RCD the specified 6 tests
x 1/2
x1 @0deg.
x1 @ 180
x5@0
x5@180
test button
preferably with all loads disconnected and test @ the RCD outgoing terminals, and only once.

your mates are either confused or dragging the job out.
 
A Rcd has operating characteristics that will apply to all the circuits,if its tested at source,the readings apply to all those circuits off that Rcd

Testing separately and externally for each circuit and including those circuit properties may show incorrect operating values
 
you test the RCD the specified 6 tests
x 1/2
x1 @0deg.
x1 @ 180
x5@0
x5@180
test button
preferably with all loads disconnected and test @ the RCD outgoing terminals, and only once.

your mates are either confused or dragging the job out.

Except, for instance, MEM RCBO's which don't like being tested at the terminals .....
 
it is easier to use a socket, and complies with the "no live working" wimp brigade.
 

Reply to RCD Testing Confusion - Help! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
327
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
792
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock