Hi all again.

Enough with helping my friend and back to the main thing, which is back to studying.

I am working on my final assessments (practice for my final L3 exam).

Big 2 story house with the following requirements (protected devices given accordingly and installation method C, clip direct assumed);

1 - Light Circuit 6A MCB

2 - Light Circuit 6A MCB

1 - Ring Main G.Floor = 32A MCB

2 - Ring Main 1st Floor = 32A MCB

1 - 3.0Kw I. Heater Circuit = 16A MCB

2 - Cooker (needs to be selected the given cable CSA of 4.00mm!, it doesn't make sense but these were the requirements, unless there's been a typo which I wouldn't be surprised). Having said that, that is why I selected a 32A MCB.

1 - 2.5kW P.V array = 16A MCB

2 - 8.5kW Shower = 40A MCB

1 = Total MCB amperage is 110A

2 = Total MCB amperage is 70A

My question is total RCD load 1 is 110A which is way above the 63A 30mA RCD and total RCD load 2 is 70A. Should the combined MCB load not exceed the RCD load capacity?

My house was done and commissioned 3 years ago and this also does not reflect in it as total load 1 is 73A and total load 2 is 54A.

I'm confused.

Any help much appreciated.

Regards,
Albert
 
Last edited by a moderator:
think i know what you mean. you're thinking of total possible load/s whereas, due to the fact that not all things will be running simultaneously, you apply diversity.
 
Hi all again.

Enough with helping my friend and back to the main thing, which is back to studying.

I am working on my final assessments (practice for my final L3 exam).

Big 2 story house with the following requirements (protected devices given accordingly and installation method C, clip direct assumed);

1 - Light Circuit 6A MCB

2 - Light Circuit 6A MCB

1 - Ring Main G.Floor = 32A MCB

2 - Ring Main 1st Floor = 32A MCB

1 - 3.0Kw I. Heater Circuit = 16A MCB

2 - Cooker (needs to be selected the given cable CSA of 4.00mm!, it doesn't make sense but these were the requirements, unless there's been a typo which I wouldn't be surprised). Having said that, that is why I selected a 32A MCB.

1 - 2.5kW P.V array = 16A MCB

2 - 8.5kW Shower = 40A MCB

1 = Total MCB amperage is 110A

2 = Total MCB amperage is 70A

My question is total RCD load 1 is 110A which is way above the 63A 30mA RCD and total RCD load 2 is 70A. Should the combined MCB load not exceed the RCD load capacity?

My house was done and commissioned 3 years ago and this also does not reflect in it as total load 1 is 73A and total load 2 is 54A.

I'm confused.

Any help much appreciated.

Regards,
Albert

You need to take into account Diversity OSG Appendix A BYB Regulation311.1 may help you understand.
 
& I wouldn't run PV onto a shared RCD protected circuit either!


Was this the regs 3 years ago?

Only asking because my house, built 3 years ago, as an RCD protecting all the sockets in the house both G. Floor and 1st Floor, almost certain that they have exceeded the 100mt sq rule for individual ring, the light circuits on 1st floor and P.V.
 
You sure your house is that big mate? There's a massive difference between 100 square metres and 100 metres square.
One thing is found in our publications, the other is not.

LOL....

I meant 100 squared meters.

Opsss, sorry.

Dream come true for my wife with a house that BIG.
 
Last edited by a moderator:
I don't have the OSG. Lost it last year and as the new edition or amendment 2015 3 rather, was due to come in this year, I just waited and never got one back.

Still haven't purchased it.

But I think this is the same as the the electricians guide to good electrical practise, page 45, there's a table for maximum demand calculations for circuits.

Am I talking about the same thing?

Many thanks,
Albert
 
Was this the regs 3 years ago?

Only asking because my house, built 3 years ago, as an RCD protecting all the sockets in the house both G. Floor and 1st Floor, almost certain that they have exceeded the 100mt sq rule for individual ring, the light circuits on 1st floor and P.V.

A g83 inverter can take upto 500ms to disconnect once the AC has been isolated.
 
Come and join me in Pedant's Corner. There's always room for one more :)

I was barley holding myself up yesterday at around 21:15 on the sofa, which is so unlike me.

Still, after an episode of 12 monkeys, I still forced myself to the PC and study until 00:30, so no wonder...

This last task B on level 3 is just in a way bizarre given that C&G expect us to know all that. I see the reason why but still, in my very limited experience I am struggling a bit and feel sorry for those in the classroom that have no experience whatsoever.

Still, I am very happy I decided to do this and have a different respect/view for electricity.

Many thanks.

Albert

P.S: The worst of it is that in the end, we all will NOT be qualified electricians as we were told 3 years ago when the course started (Level 2).
 
Last edited by a moderator:

Reply to RCD total load vs MCBs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
570
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock