Discuss RCD Trip Times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

BigSi

-
Reaction score
55
[FONT=&amp]I was talking to one of my friends who just had his NICEIC DI assessment (about five months ago). We got talking about RCD trip times, because he was told that what he believed in (and myself) was wrong?[/FONT]
[FONT=&amp]
RCD (30mA) TRIP TIMES (17[SUP]th[/SUP] Edition Regulation 411.3.2.2. – Table 41.1)[/FONT]


[FONT=&amp]For a nominal a.c.voltage not exceeding 230v, disconnection times are not exceed[/FONT]


[FONT=&amp] For a final circuit not exceeding 32A in a TT system 200ms (0.2 sec)[/FONT]

[FONT=&amp] For a final circuit exceeding 32A in a TT system 1000ms (1 sec)[/FONT]

[FONT=&amp] For a distribution circuit in a TT system 1000ms (1 sec)[/FONT]

[FONT=&amp]For a final circuit not exceeding 32A in a TN system 400ms (0.4 sec)[/FONT]

[FONT=&amp] For a final circuit exceeding 32A in a TN system 5000ms (5 sec)[/FONT]

[FONT=&amp] For a distribution circuit in a TN system 5000ms (5 sec)[/FONT]


[FONT=&amp]He was also saying that when you peform an Inspection & Test, if the consumer unit isn’t a 17[SUP]th[/SUP] edidion board, it needs upgrading. [/FONT]

[FONT=&amp]My take was that as long as it complied with the current regulation at that time (16[SUP]th[/SUP] Eddition), and didn’t pose any additions risks (all circuits protected by RCD’s, etc), than it would be fine. Or give it a Code 3 – improvement recomended. [/FONT]
 
Must make extra sockets an expensive job.. you cant insist on a CU change on every job. As long as your work complies then its fine. No Rcd would get code 3 unless its feeding sockets for outside then code 2
 
You will attend lots of premises that don't even have rcd,s but that doe not mean that the system is unsafe or needs changing. We can recommend as good safe practice but there is no compulsion on the owner to upgrade.
Ben
 
so what about older installations with no RCD whatever. still a code C3 unless as bigbad pointed out a code C2 if fo outside use.
 

Reply to RCD Trip Times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
886
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock