Discuss RCD tripping- earth neutral fault in the Australia area at ElectriciansForums.net

This rat thing is making me giggle but i have had on two occasions cables being damaged by rodents nibbled right into the cable its especially frustrating when you have just done a board change and circuits are now rcd prot and you have to start looking for a little mouse bite in a cable little blighters.:eek:
 
they cause a bit of bother alright

one bit clean through a 3*1.5 flex a while back on a job
plenty of bother with rats+mice when i worked on ind. maintenance-caused various breakdowns
 
Last edited by a moderator:
Neutral to Earth fault (short circuit) plastic outer cover bitten and damaged, short circuiting the Neutral to Earth. The RCD trips (even if you keep all the MCBs off). No way to get power back .. either you find the fault and repair it or bypass the RCD (not recommended)
 
and the fault was......??????
Neutral to Earth fault (short circuit) plastic outer cover bitten and damaged, short circuiting the Neutral to Earth. The RCD trips (even if you keep all the MCBs off). No way to get power back .. either you find the fault and repair it or bypass the RCD (not recommended):)
 
an R C D works on balance ; for example if you have 10 amps going through the live you must have 10 amps returning through the neutral if their is any difference it can only be going to one place EARTH the R C D will detect this and trip. unplug all appliances . then plug them back in one by one until it trips most likely white goods agree with everyone else never bypass an R C D a bad move
 
yep -never bypass an rcd

N-E fault usually trips rcd when you plug in a class2 appliance on a protected circuit

can you explain why this happens???

i came across a similar situation but class one equipment (earthed) tripped the RCD even with the ring mcb off
and class 2 equipment worked fine with the mcb on/off

pretty sure its down to a earth / neutral fault but cant figure out how class one trips the RCD as soon as its plugged in?????
 
it trips with the mcb off because you have zero current flowing in the line. anneutral/earth fault wilcause current to flow throgh the neutral to earth, thus causing inbalance. with class 2 equipment, the earth is not connected to the appiance, so no fault current. sssssssimple.
 
it trips with the mcb off because you have zero current flowing in the line. anneutral/earth fault wilcause current to flow throgh the neutral to earth, thus causing inbalance. with class 2 equipment, the earth is not connected to the appiance, so no fault current. sssssssimple.

If you have zero current flowing in the Line, how is there anything flowing from neutral to earth to cause an imbalance - I thought the neutral was 0v and earth was 0v.....so no flow.

What difference does it make if it's Class 2 and no earth - the fault current doesn't have to flow back down the 'earth' (or should I say CPC) - it can flow anywhere and still cause an imbalance between L & N.......it could flow through you!!...which is kind-of the whole point of RCD protection.:D

So....maybe not that sssssssimple.:)
 
The mcb only switches the line. The neutral is still connected to the neutral bar. So with current flowing through other circuits that are covered by the same rcd, some of that current can flow along the neutral bar, up the neutral of the circuit you believe to have been isolated, through the neutral of the plug/socket where the faulty appliance is plugged in, up the neutral of the faulty equipment and then down the earth of that equipment via the N-E fault within that equipment.
 
Last edited:
Can I ask stupid question in this subject please? Could a Live/Earth fault cause tripping RCD also? If you had a rcd protected board is it possible for the rcd to trip and not the mcb on a live/earth fault? Thanks
 
Can I ask stupid question in this subject please? Could a Live/Earth fault cause tripping RCD also? If you had a rcd protected board is it possible for the rcd to trip and not the mcb on a live/earth fault? Thanks
Yes. The RCD trips when the current flowing in L and N are different by more than 20ish mA.
So if there is a L to E leakage of 10's of mA you would expect the RCD to trip, but not the MCB.

it sometimes happens that appliances with a heating element (immersion heater, washing machine, kettle, oven, etc) develop a leakage to earth, which will trip an RCD, but not the MCB.
Also lots of loads that individually have EMI (interference) filters in them, all connected to the same circuit, can result in excessive leakage to earth, which can cause nuisance tripping of an RCD.
 
Last edited:
Yes. The RCD trips when the current flowing in L and N are different by more than 20ish mA.
So if there is a L to E leakage of 10's of mA you would expect the RCD to trip, but not the MCB.

it sometimes happens that appliances with a heating element (immersion heater, washing machine, kettle, etc) develop a leakage to earth, which will trip an RCD, but not the MCB.
Thanks for that. I had a db which main rcd had tripped. I turned all circuits off,reset rcd and turned on one at a time turns out it was an immersion heater. So was curious what may have caused the rcd to trip and not mcb. Thanks again
 

Reply to RCD tripping- earth neutral fault in the Australia area at ElectriciansForums.net

Similar Threads

Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
576
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
329
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock