Discuss RCD tripping issue on ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
First time poster go easy on me.

Got a call out to a job today, got told the RCD was tripping. Even when no appliances plugged in. And so it was intermittently about every 20 mins. Only two ring circuits on the RCD, on one of the rings im getting continuity across line and netural on both legs. Its not taking the MCB out, no fault across the earth.

Tested the RCD for nuisance tripping all passed fine.

Cant get my head around why with a permanent short the MCB wont trip? Going back tomorrow morning for further investigation and feeling as if i should suggest re wire of sockets due to reasonably low IR readings anyway.

Any thoughts would be appreciated.
Cheers
 
Welcome to the forums.

When you say continuity... what kind of readings are you getting Line to Neutral? I'm suspecting they are not shorts but some appliance.

Why do I say that? Because a line/neutral fault won't trip the RCD because even under a direct short, the current flowing in line will be the same as that flowing in neutral and the RCD will quite happily sit there.

What IR readings were you getting?
 
Cant remember the exact values on continuity, but it was a high level of resistance.

There are some kitchen appliances left to be checked, but those are on fused spurs so i suppose a fault could still come back up the netural if only single pole switch.

IR getting >0012 and i know its technically acceptable but its pretty low and makes me feel a bit uneasy.
 
If you're getting continuity but a high resistance, then it's more like to be something plugged in/connected.

The IR reading is that L and N to earth, or L to earth, N to earth, L to N? And is that 1.2Mohms?
 
Is there any chance there's an exterior light wired out the back of one of the sockets that might have damp in it? I've seen this happen many times
 
First time poster go easy on me.

Got a call out to a job today, got told the RCD was tripping. Even when no appliances plugged in. And so it was intermittently about every 20 mins. Only two ring circuits on the RCD, on one of the rings im getting continuity across line and netural on both legs. Its not taking the MCB out, no fault across the earth.

Tested the RCD for nuisance tripping all passed fine.

Cant get my head around why with a permanent short the MCB wont trip? Going back tomorrow morning for further investigation and feeling as if i should suggest re wire of sockets due to reasonably low IR readings anyway.

Any thoughts would be appreciated.
Cheers
Find the fault, fix the fault. Don't just go rewiring a circuit because there is a fault on it.
As the fault is still not found it could be literally anything, faulty appliance, central heating pump, damp, damaged cable and many more. Find where the fault is first, then come up with the solution.
 
Cant remember the exact values on continuity, but it was a high level of resistance.

There are some kitchen appliances left to be checked, but those are on fused spurs so i suppose a fault could still come back up the netural if only single pole switch.

IR getting >0012 and i know its technically acceptable but its pretty low and makes me feel a bit uneasy.
IR > 0012??
 
I only ever read the post buzz, never the comments lol. For all I know I could constantly be repeating what others say.....


Appliance still plugged in. Cooker hood, FCU will be behind chimney.
Even turned off at socket, can still get an N-E fault to trip rcd.
Have you checked the mcb isn’t at fault?

Buy yourself a notepad and a pencil. For taking notes.
 
Is the heating fed by one of these circuits? If the RCD trips yet you've got good IR readings that implies an intermittent fault which can be caused by e.g. the heating/water heating coming on and there's a faulty component (pump, valve, boiler pcb, immersion element), or a compressor motor kicking in.

A healthy ring circuit has a natural earth leakage of about 3mA, the power supplies for modern equipment such as TVs, PCs, phone chargers etc also have quite high earth leakage; when it trips it could it be the sum of these exceeding 30mA.

Does it trip when you're there and have disconnected everything, or when stuffs plugged in/switched on?

Is there e.g. a PIR external light fed via a FCU on the circuit?
 

Reply to RCD tripping issue on ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock