Discuss RCD Tripping MCB's on Circuit OK in the UK Electrical Forum area at ElectriciansForums.net

Can't believe some of the responses I've read to this.

The MCBs aren't tripping because it's an earth leakage fault not a current overload fault.
The fault isn't definitively a N-E RI fault but could still be a L-E RI fault.
The ONLY way to find out is to use an insulation resistance tester on each of the circuits to find the one with low IR, then remove all connected devices from that circuit (you may have double pole sockets but how can you be certain they are all DP sockets?, one may have been replaced/fitted with SP).
Do a continuity test between live and neutral to prove all devices are disconnected.
Then test the circuit again, if you've still got a low IR the fault is in the fixed wiring/accessories. If the IR reading is OK then it was one of the connected devices. Use the IR tester on each to find out which one.
 
Can't believe some of the responses I've read to this.

The MCBs aren't tripping because it's an earth leakage fault not a current overload fault.
The fault isn't definitively a N-E RI fault but could still be a L-E RI fault.
The ONLY way to find out is to use an insulation resistance tester on each of the circuits to find the one with low IR, then remove all connected devices from that circuit (you may have double pole sockets but how can you be certain they are all DP sockets?, one may have been replaced/fitted with SP).
Do a continuity test between live and neutral to prove all devices are disconnected.
Then test the circuit again, if you've still got a low IR the fault is in the fixed wiring/accessories. If the IR reading is OK then it was one of the connected devices. Use the IR tester on each to find out which one.
Right RI fault?
 
Can't believe some of the responses I've read to this.

It could simply be accumulated earth leakage from a variety of sources of equipment on the circuit(s) - you will not find this out simply by doing IR tests.......... you need a clamp meter..................................

Seen this on a number of occasions.........
 
It could simply be accumulated earth leakage from a variety of sources of equipment on the circuit(s) - you will not find this out simply by doing IR tests.......... you need a clamp meter..................................

Seen this on a number of occasions.........
Preferably one that reads miliamps
 
I'm with Tel on this. New builds are generally built like an Ikea wardrobe, no solid backbone, no integrity, just done to the lowest common denominator. The fact that we as a society have taken generations to master all aspects of building, and then accepted the carp that is produced is woeful. Yes, economics (and greed) play a part, but the standards we currently accept are sad.

So, get it knocked down and build a proper house!! Or move....

Re the OP; Murdochs suggestions sound a good plan to me.
 
Unfortunately, the lottery numbers haven't come through yet so moving will have to wait until this weeks Euromillions draw.

In the mean time - Ok here it goes, I'll wait for the onslaught. "Would it help (if room in the CU) to replace the MCB's with RCBO's, to determine the circuit that may be causing the issue".
 
Shouldn't be necessary. Apart from the cost, the risk is a second fault may be introduced doing the change. I prefer to fix known faults first :)
 

Reply to RCD Tripping MCB's on Circuit OK in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
554
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
808

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock