Hi All

I wonder if somebody can help.

In our domestic CU one of the RCD's keeps tripping out without any of the MCB's tripping. When I reset the RCD it resets fine without any problems. All is ok for an intermittent period (could be days or hours and it trips again).

I think from the forum this is indicating a N-E fault and I need to maybe do some investigative work on each of the MCB protected circuits to try and diagnose which appliance (if any) is causing the problem. However I'm not sure if that will diagnose the issue as I've learnt the RCD shares a neutral bar with all of the affected circuits. Basically I'm not sure of the most logical way to go about doing the testing.

The RCD usually resets fine without any MCB tripping, however a couple of times one of the MCB's tripped when I reset the RCD (The circuit included some downstairs sockets/fridge/oven/alarm). The MCB reset fine though and I'm wondering if this was a red herring as only the fridge and house alarm were on at the time.

This is a new house build with full electrical certifications and only two years old. I don't want to call the electricians out for a simple fix.Any ideas please?

Thanks
 
Might not be a neutral fault, may just be an appliance that is breaking down. Such as a compressor on a fridge/freezer, heating element going in a kettle or water tank. Washing machine, tumble driers are another good culprit.

Not only that but you could have a few items with cumulative earth leakage that's leaking just enough combined to go over the RCD's threshold.

Have you noticed any correlation between when it trips and you undertaking certain tasks?

Unfortunately intermittent faults can be a real pain to find even with proper test gear.
 
I had this issue a few months back, happened when turning the oven in cooker on, the heating element was on its way out. RCD would trip within seconds of me turning it on. cost of finding a suitable part and time involved, i just popped along to curry's and bought a new one.
I would say turn MCB's off leaving just one on and then go round unplugging things. eventually you will likely find the offending device
 
Thanks for the replies.

JCB option might have wait for the moment!

No pattern I'm afraid. Just come back from hols and switched most of the sockets off before I went. Only the fridge and house alarm were connected really to the possible 'faulty' MCB circuit. Came back to find the RCD tripped.

Can somebody suggest a test procedure please. Should I be disconnecting Neutral sides of MCB's etc to try and diagnose?
 
You could find the offending circuit by removing neutrals but it would only indicate which circuit if the fault was there continuously

I will stick my head on the line here and suggest your fridge is causing the tripping when its compressor is switched into use

If you were to run this suspect appliance(or any other for that matter) from a socket fed by the other Rcd (using an extension lead) and see if you can get an appliance to cause the other Rcd to trip.it will be a process of elimination but you should get there
Does this Rcd also supply a light circuit with a outside light perhaps
 
Unless you know that you have double pole sockets, just switching off may not prove anything. Bouble pole sockets break both the live and the neutral conductors, single pole only the live so would still leave the neutral connected.
 
Your best course of action IS to keep a log of when it happens ......... then when you call a sparky in, they will have something to go on.............................

BUT I warn you it could be accumulated earth leakage so random appliances could push this over the threshold for the RCD....

What the other have said all apply too.
 
Hi All

I wonder if somebody can help.

In our domestic CU one of the RCD's keeps tripping out without any of the MCB's tripping. When I reset the RCD it resets fine without any problems. All is ok for an intermittent period (could be days or hours and it trips again).

I think from the forum this is indicating a N-E fault and I need to maybe do some investigative work on each of the MCB protected circuits to try and diagnose which appliance (if any) is causing the problem. However I'm not sure if that will diagnose the issue as I've learnt the RCD shares a neutral bar with all of the affected circuits. Basically I'm not sure of the most logical way to go about doing the testing.

The RCD usually resets fine without any MCB tripping, however a couple of times one of the MCB's tripped when I reset the RCD (The circuit included some downstairs sockets/fridge/oven/alarm). The MCB reset fine though and I'm wondering if this was a red herring as only the fridge and house alarm were on at the time.

This is a new house build with full electrical certifications and only two years old. I don't want to call the electricians out for a simple fix.Any ideas please?

Thanks
Are you suggesting he should be digging for this fault himself
No if I know Tel like I think I know him he means knock the gaff down and start over, I think, Tel!!!
 
I think he did mean know the gaff down!!!

Not sure if I have double or single pole sockets, will have to check. I will keep a log and follow the test procedures suggested - thanks.

There are some outside sockets IP66 standard on the circuit.
 
Yes I can. They are on a switched connection so I can turn off just the outside sockets from inside. I only put them on when required as they are at the front of the house. They have been off every time RCD trips.
 
You could find the offending circuit by removing neutrals but it would only indicate which circuit if the fault was there continuously

I will stick my head on the line here and suggest your fridge is causing the tripping when its compressor is switched into use

If you were to run this suspect appliance(or any other for that matter) from a socket fed by the other Rcd (using an extension lead) and see if you can get an appliance to cause the other Rcd to trip.it will be a process of elimination but you should get there
Does this Rcd also supply a light circuit with a outside light perhaps

Agree with Des, that fridge is the first thing I'd rule out, before trying anything else.

Nice track by the way Pete :cool:
 
A bit of a drastic action to resolve a fault.
the idea behind the post was that it would not only solve his electrical problem, it would also fix the many issues of a new build, e.g. dry lining, weetabix floors, unseasoned timber, wonky roof trusses that bar access to attics,, 3 tons of insulation, studded walls, and all the other cheap and nasty practices that came in on the 1960's and 1970's, along with mowtown, and rapp "music".
 
the idea behind the post was that it would not only solve his electrical problem, it would also fix the many issues of a new build, e.g. dry lining, weetabix floors, unseasoned timber, wonky roof trusses that bar access to attics,, 3 tons of insulation, studded walls, and all the other cheap and nasty practices that came in on the 1960's and 1970's, along with mowtown, and rapp "music".
If you think they were bad then you should see some of the new builds done now !.
 
QUOTE - [ They have been off every time RCD trips.

If power goes to the light fitting and then via a switch loop,
then moisture can still get in and cause problems even when the switch is off !
 
Can't believe some of the responses I've read to this.

The MCBs aren't tripping because it's an earth leakage fault not a current overload fault.
The fault isn't definitively a N-E RI fault but could still be a L-E RI fault.
The ONLY way to find out is to use an insulation resistance tester on each of the circuits to find the one with low IR, then remove all connected devices from that circuit (you may have double pole sockets but how can you be certain they are all DP sockets?, one may have been replaced/fitted with SP).
Do a continuity test between live and neutral to prove all devices are disconnected.
Then test the circuit again, if you've still got a low IR the fault is in the fixed wiring/accessories. If the IR reading is OK then it was one of the connected devices. Use the IR tester on each to find out which one.
 
Can't believe some of the responses I've read to this.

The MCBs aren't tripping because it's an earth leakage fault not a current overload fault.
The fault isn't definitively a N-E RI fault but could still be a L-E RI fault.
The ONLY way to find out is to use an insulation resistance tester on each of the circuits to find the one with low IR, then remove all connected devices from that circuit (you may have double pole sockets but how can you be certain they are all DP sockets?, one may have been replaced/fitted with SP).
Do a continuity test between live and neutral to prove all devices are disconnected.
Then test the circuit again, if you've still got a low IR the fault is in the fixed wiring/accessories. If the IR reading is OK then it was one of the connected devices. Use the IR tester on each to find out which one.
Right RI fault?
 
Can't believe some of the responses I've read to this.

It could simply be accumulated earth leakage from a variety of sources of equipment on the circuit(s) - you will not find this out simply by doing IR tests.......... you need a clamp meter..................................

Seen this on a number of occasions.........
 
It could simply be accumulated earth leakage from a variety of sources of equipment on the circuit(s) - you will not find this out simply by doing IR tests.......... you need a clamp meter..................................

Seen this on a number of occasions.........
Preferably one that reads miliamps
 
I'm with Tel on this. New builds are generally built like an Ikea wardrobe, no solid backbone, no integrity, just done to the lowest common denominator. The fact that we as a society have taken generations to master all aspects of building, and then accepted the carp that is produced is woeful. Yes, economics (and greed) play a part, but the standards we currently accept are sad.

So, get it knocked down and build a proper house!! Or move....

Re the OP; Murdochs suggestions sound a good plan to me.
 
Unfortunately, the lottery numbers haven't come through yet so moving will have to wait until this weeks Euromillions draw.

In the mean time - Ok here it goes, I'll wait for the onslaught. "Would it help (if room in the CU) to replace the MCB's with RCBO's, to determine the circuit that may be causing the issue".
 
Shouldn't be necessary. Apart from the cost, the risk is a second fault may be introduced doing the change. I prefer to fix known faults first :)
 

Reply to RCD Tripping MCB's on Circuit OK in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
610
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
388
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
861

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock