Discuss RCD Tripping, Nothing in Sockets, no load... what now? in the Australia area at ElectriciansForums.net

would love to know the original tripping times of the old RCD as the only time ive found them to give this type of pain in the butt tripping is when they trip at less than 10ms at x1. dont suppose you know?
 
Hi Bigbaddave, on page 4 i said he fitted a new RCD switch, since then touch wood no more faults.
 
Last edited by a moderator:
Neutral earth short as well as a crossed neutral in the consumer unit, if there is a excessive total length of cable on the RDC, the capacitance currant cause it to trip, say if the capacitance from live to earth approaches say 300nF (300 nano farads).
 
raise_thread.jpg

......
 
Cold possibly be a loose connection or loose breaker on the shower circuit, are there any sigas of burning or is the connection hot to touch, with theach power turned off of course
 
Wow, ok this thread was raised and keep receiving email notifications of new replies lol

The issue was fixed by replacing the RCD fuse thing in the fuse box... ever since... no issues at all - so it seemed like it was a little toooo sensitive.

Lay this poor thread to rest, I appreciate all of your replies :)
 
Wow, ok this thread was raised and keep receiving email notifications of new replies lol

The issue was fixed by replacing the RCD fuse thing in the fuse box... ever since... no issues at all - so it seemed like it was a little toooo sensitive.

Lay this poor thread to rest, I appreciate all of your replies :)


I'll close the thread, its been a while and request acknowledged :)
 

Reply to RCD Tripping, Nothing in Sockets, no load... what now? in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
779
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
450
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
791
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock